Got a domestic install with client requesting CU upgrade. Tails are 16mm, EC 10mm, and buried in structure between meter and fusebox. Rating of DNO cutout fuse not known. Ordinarily I would upgrade the tails & EC to 25/16 as a matter of course (domestic load includes an outdoor hot tub as well as the usual sockets/cooker/immersion type stuff, don't recall if electric shower present) but routing them through the existing route of the 16mm tails looks like a non starter and I can't see a practical alternative route. The meter box is small and absolutely chocker with no space in there to add a separate fused cutout. Adding a fused cutout next to the replacement CU (in downstairs cloakroom) would probably be doable but cluttered/messy.

Installing a 63A MCB in the new CU, suitably labelled, immediately downstream of the main switch and feeding all RCDs/final circuits...good/stupid idea?
 
Seeing as the vast majority of domestic installations don't need anywhere near a 100A DNO supply and that 16mm tails are generally good to 80A , i can't see any problem. Why would you automatically upgrade tails to 25mm as a matter of course, for what reason??....
 
Seeing as the vast majority of domestic installations don't need anywhere near a 100A DNO supply and that 16mm tails are generally good to 80A , i can't see any problem. Why would you automatically upgrade tails to 25mm as a matter of course, for what reason??....

Because I have no control over what cutout fuse the DNO chooses to fit at a later date and I have no control over the client choosing to run all their final circuits close to full capacity simultaneously (however many times I calculate for diversity).
 
how long have these 16mm tails been in without signs of any damage? sod it, leave well alone.
 
Because I have no control over what cutout fuse the DNO chooses to fit at a later date and I have no control over the client choosing to run all their final circuits close to full capacity simultaneously (however many times I calculate for diversity).

Which is NOT your problem.

Pull fuse, but I'd leave the 16mm tails in place FWIW
 
Because I have no control over what cutout fuse the DNO chooses to fit at a later date and I have no control over the client choosing to run all their final circuits close to full capacity simultaneously (however many times I calculate for diversity).
So because at some unspecified point the DNO might decide willy nilly to put a 100A fuse in you're going to upgrade?
Shouldn't you also then consider the possibility of a 200A going in? Or a 3 phase head being installed?
How likely is it that this fuse upgrade will come out of the blue?
How likely is it that the client will run all their circuits at or close to the full demand placed on them?
 
...Nice twisting,and respect due for red zip-ties,having noticed the only potential risk being conductor identity :conehead:
 
So because at some unspecified point the DNO might decide willy nilly to put a 100A fuse in you're going to upgrade?
Shouldn't you also then consider the possibility of a 200A going in? Or a 3 phase head being installed?
How likely is it that this fuse upgrade will come out of the blue?
How likely is it that the client will run all their circuits at or close to the full demand placed on them?

Haway Trev, DNOs don't do willy nilly things. They always check their Ze when replacing a knackered head, and always have their own 16mm cables on their vans. DNOs are many things but never willy nilly!!

Nick, am sure the 16mm will be fine, check the loading obviously. It's no wonder we are running out of copper!!
 
So because at some unspecified point the DNO might decide willy nilly to put a 100A fuse in you're going to upgrade?

I guess what it comes down to is this: how legit/reasonable is it to rely on the rating of the presently-installed DNO fuse to protect the tails? As I understand it, the DNO fuse is there to protect their cable/equipment, and any protection it gives to the consumer side of the installation is a side effect. If at a later date they were going to uprate the fuse, such that the 16mm tails would no longer be protected by it, are they under a clear duty to consider this and act accordingly?

How likely is it that the client will run all their circuits at or close to the full demand placed on them?

Like any risk that has to be managed based on the likelihood of it happening and impact if it does. Impact of extended overload of the tails could be pretty catastrophic. How likely, well, we have to be thinking over a timescales of decades I guess (imagine a cold Christmas Day with the cooker going full blast and people getting showers, when the boiler packs up and so five electric heaters and the immersion get turned on). Not inconceivably unlikely.

None of this is meant to sound pretentious and up myself by the way, that's just the way I write :)
 
Last edited by a moderator:
Don't send ya head into spasm worrying about 16mm tails. As mentioned above they are good for upto 80a and i wouldn't mind betting that that your main fuse is 60a 1361 type iib anyways so leave alone. You'd be doing well to blow even a 60a fuse from normal household demands.
 
Nick the DNO fuse is there to protect their kit so if a 40/60/80 amp fuse has been quietly getting on with the task and not bothering anyone what possible motivation could they have for changing it? I've got a 16 amp RCBO on a radial circuit in my house, it's been doing what it does for about 6 years now, think I should change it for a 20 just for the hell of it?
I don't think you're pretentious by the way, wrong, misinformed, ill advised perhaps but not pretentious :)
 
Nick the DNO fuse is there to protect their kit so if a 40/60/80 amp fuse has been quietly getting on with the task and not bothering anyone what possible motivation could they have for changing it? I've got a 16 amp RCBO on a radial circuit in my house, it's been doing what it does for about 6 years now, think I should change it for a 20?

of course you should change that 16A for a 20A. what about when you add the 10kW shower to that radial?
 
Nick the DNO fuse is there to protect their kit so if a 40/60/80 amp fuse has been quietly getting on with the task and not bothering anyone what possible motivation could they have for changing it? I've got a 16 amp RCBO on a radial circuit in my house, it's been doing what it does for about 6 years now, think I should change it for a 20 just for the hell of it?
I don't think you're pretentious by the way, wrong, misinformed, ill advised perhaps but not pretentious :)

I can't think of a reason, but that doesn't mean there isn't one. Big organisations move in mysterious ways. I would be happier with some kind of assurance that I am perfectly within my rights to rely on the DNO fuse to protect the tails.

20 is a rounder number than 16 if you tend to think in decimal?

Are you sure you're not ill advised when you advise me that I'm being ill advised? ;)
 
As an experiment I ran my flat on a 16A MCB for two months. Never tripped once.

If you look for the diversity figures UKPN use they’re unbelievably low.
 

Reply to Protecting 16mm tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
651
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size...
Replies
6
Views
2K
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
790

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock