animox

Hi
In commercial location I need to run 8 individual RCD protected circuits to 8 D/Skt outlets, each run is in 2.5 singles in plastic conduit about 20m max in length.

My question is can I run a single cable earth ring to each skt and if so what size should it be, Worst case is all 8 skts pulling 3A each.

Any guidance appreciated, cheers
 
Why are you running single socket radial circuits for in the first place?? I hope you're not trying to pull in 8 circuits into a single 20mm conduit ?? If this is for IT loads the answer is NO!!
 
if you are wanting to individually protect each socket, why not run in a RFC and use RCD sockets?
 
I need individual rcd protection for each skt, so one circuit in fault doesn't effect the rest.
The conduit run is 75 x 75 sq and 20mm to each skt

Each circuit will run a small pump and some fluorescent uv tubes

Local rcds skt on a 2.5 RFC would solve the problem,
But I wanted to utilise a bank of rail mounted rcds already installed, rather than buying 8 new IP66 rcd skt outlets.
 
for what it costs, run separate cpc's to each socket outlet.
 
I need individual rcd protection for each skt, so one circuit in fault doesn't effect the rest.
The conduit run is 75 x 75 sq and 20mm to each skt

Each circuit will run a small pump and some fluorescent uv tubes

Local rcds skt on a 2.5 RFC would solve the problem,
But I wanted to utilise a bank of rail mounted rcds already installed, rather than buying 8 new IP66 rcd skt outlets.

That's a big piece of conduit
 
we know it's mm, but don't you mean trunking. ?

- - - Updated - - -

oruse the metal containment as cpc.
 
Sorry Plastic trunking, its a commercial uv sterilization plant for shell fish.

Thanks for your help guys
 