K

Kev2632

While doing the r1 and r2 loop test on a ring main they always say at least the r2 too be a larger reading than the r1, because of the cable size difference?.

why is the earth reading higher, I thought the bigger the area of the core, it would have more resistance than that off of 1.5mm earth???
 
Think of the water analogy, a big diameter pipe lets water flood through and a small pipe holds it back. the same with resistance in cables..
 
just think of the smaller cable restricting flow. edd's analogy sums it up. another analogy is motorways. when there is lane closures, the resistance to the flow of traffic is increased.
 
yes and also if doing an R1 R2 on a circuit using DC then the value is measured in resistance. However, for live testing....such as an earth fault loop test...then the value is refered to as impedence...as its using AC......
 
always a bit confusing to start, a copper pipes length is increased and then csa halfed whats the effect on resistance blah
 
Stick with the theory....

Resistance, R = p * (l/A)

p (greek letter rho) is the resistivity of copper, a constant
l is conductor length
A is cross sectional area of the conductor

so longer the length, higher the resistance
and greater csa, A, lower the resistance.



Here endth today's lesson.
 
OP you need to grasp the idea of resistivity using some of the explanations that are given i personally use the water idea as its the way i was taught, if you had a 1m conductor if it doubled in length the resistance would double, if you doubled the cross sectional area the resistance would halve...
 

OFFICIAL SPONSORS

Back
Top