Righto, i'll have wait till next weeks overtime comes in then. :)

Yeah, a tad pricy!

Shopping around you can get something to do up to 750A for the £5k mark - my initial prices were a bit off.

I had complete access to the programma range and regularly used the top end test kit - I worked for a protective relay manufacturer and consultancy, it was a bit of a shock when I left and needed to buy or hire the kit myself.

I am now more selective when I hire kit!

If the mcbs were mandated to be tested, then simpler test units at reasonable prices would become available, as it is, it's a small specialist market!
 
Now that's closer my budget, do you do one in blue?
Did get any reliable results from it?
For an extra £99.99 I’ll paint it any colour :) .
I did have fun with it, that part was reliable. At the time I had a few MCBs that had been replaced as they seemed to be soft and I wanted to see if I could confirm it. I could load to their rated values and let them run. The MCBs were for the recycle anyway, so it was just for fun.
 
I got a job a few years ago to go offshore to an oil platform to do a week of nights testing 16A mcbs for the trace heating systems, did a couple of hundred of them, good money but very boring.
I have my own sverker but it is used mainly for HV protection relays.
 
Funnily enough, it's something that's gone through my mind over the years. My late father had a good old fashioned stick welder with a big knob on the front that winds part of the transformer core in/out to adjust the current. I reckoned that would probably make basis of a test set ;) Maybe with a step-down auto-transformer in front of it.
I'm thinking you need to be able to do 1x to check for false tripping, 2x to check for thermal trip, and 5x or 10x to check the magnetic trip. I had in mind a contactor to bypass the current round the under-test MCB while setting tbe current, then release the contactor and see how long it takes to trip. Wouldn't be precision timing, just "yeah it trips" sort of manual observation.
 
You are in the right area Simon. However I don't know what type of waveform a welder puts out. The proper test kit is designed to do a true sine wave right across the range, also an automatic timer is pretty much essential.
If you can get hold of the technical details of the MCB you should find a curve which plots time against current up to the point where the instantaneous trip takes over. So you put in a set current and check that it trips at the correct time, then do a single test at 10% over the instantaneous and check for an immediate trip. The problem is that the overload part is thermal so you have to let it cool between tests, so the quick and dirty way is to inject current about half way up the thermal curve and check the time then do the magnetic at 110% and check it trips sooner than the thermal curve extrapolated to that value.
 
I'd be expecting a fairly accurate sine wave given that it's a transformer - at least, connecting before the rectifier as I'd be planning to do.
 
Test sets often have toroidal cored transformers to ensure a purer waveform. Why to rectifier? MCBs are designed to work on ac, their voltage rating is reduced on dc.
 
The kettle route , would induce high load arc wear
breaking load at both high voltage and overload current.
(Pretty sure the "expensive" testers are reducing this potential contact Wear !)
 
Given the problems of testing such as high cost equipment, wear and tear on the device, downtime of the circuit with having isolate device etc surely it's a better option just to replace with new. Not sure what you guys are getting charged for MCB's but we're paying around a quid for a 4.5kA Chinesium single pole and less than 2 quid for a European brand.
 