brucey2343

Hi,

My QS believes an RCBO provides fault protection only, and we have to enter N/A on the test certs for the additional protection. Is this correct? We deal with TN-C-S and TN-S domestic. I assumed it provided both

Thanks!
 
If it's a 30mA trip current then no, it is most definitely incorrect.

It provides fault protection via the MCB and additional protection via the RCD element, and of course earth fault protection where you are unable to achieve a sufficiently good Zs (typically TT systems).
 
So a 30ma RCBO does provide fault and additional protection? Is there somewhere this is in writing?
 
I am referring to the schedule of inspections, 4.19 "RCD(s) provided for additional protection/requirements - includes RCBOs (411.3.3; 415.1). 411.3.3 states additional protection must be provided for sockets not exceeding 32A and mobile equipment for outdoors not exceeding 32A (I assume this to be plug-in lawnmowers etc). So I am correct, 30mA RCBOs are both ticks on 4.18 and 4.19 of the inspections?
 
And what he believes an RCBO is.

And if he says combined MCB and RCD, then ask him why it doesn't provide additional protection is it has a 30mA trip current. Will be very interesting to hear his reasoning.
 
Hi,

My QS believes an RCBO provides fault protection only, and we have to enter N/A on the test certs for the additional protection. Is this correct? We deal with TN-C-S and TN-S domestic. I assumed it provided both

Thanks!
QS needs re educating
 
It depends on what the purpose of the RCD is for. If it is for a high Zs then it is for fault protection but only if additional protection is not required. If it is for high Zs and for example sockets then it is still for both fault and additional protection.
 