well its on a 3phase TT system with one supply board and to consumer units, access to supply board is restricted
 
You will probably find that a 100ma s type will be a shed load cheaper to buy than a 300ma ( Thats what i have found in the past anyway ! ) , and unless they are planning to install air / ground source heating or inverter drives then i can not think why it needs to be 300ma ?
You may want to think about going for a stand alone one in its own enclosure as well , as not all boards have them available as a extra option .
 