ramp the bloody thing with loads off.....make a note of the value
re-ramp with loads/finals connected....subtract the value obtained from the 1st value obtained....this will be the approx earth leakage....
you may have a leakage clamp..i dont know...
but i would be proving the device before owt else....
then move on from there....
 
I had a similar issue shortly after I moved into my current house. IR tested all final circuits and found the cable supplying the kitchen extractor fan was at fault. Turned out the chase for the final section of the cable run had been filled in with cement for some reason (as well as being run diagonally) and it was that stretch that had developed the IR fault (N-E).
 
the obvious one here of course is to IR finals...
otherwise its just chasin your own arse with guesswork...
 