UK RCD trips when i flip down while i change sockets

Hi i am modernizing the single sockets in the living room and so i started to flip the breakers which says ground floor sockets. To my surprise i still had electricity everywhere on all floors! Thank God I checked.
Then I flipped the other breaker which was labeled kitchen sockets. That did the job as there was no electricity anymore on the ground floor on all sockets including the kitchen.
But then wife yelled she had no power upstairs. As i checked the RCD for all 3 breakers had flipped. Upon testing I discovered that when i flip the first two breakers the RCD trips.
Whats going on???!! What could be the possible wiring that can cause this? Thats the quality of working class homes in uk.
Edit: I tested some more today and now rcd does not trip but if i turn off the breakers and touch the isolated sockets live and neutral wires the rcd trips...so it must have tripped before even the curcuit was isolated. So it wasnt isolated till upstairs sockets were also off. What to make of all this? At the board the socket circuits are two rings and one linear if number of wires are indication
 
Last edited:
Photo of board might help, but I am expecting an rcd serving several mcbs.

Isolating the mcb only breaks the live conductor… but when you are working on sockets, touching neutral to earth, or touching neutral with fingers may cause the rcd to trip as it should. It is sensing a fault between neutral and earth.

Mislabelling of consumer units is a common problem and not unique to “working class” homes as you put it.


I’ve seen some pretty upmarket builds with the same problems… it’s like no testing was done afterwards… just bang test and walk away.
 
Photo of board might help, but I am expecting an rcd serving several mcbs.

Isolating the mcb only breaks the live conductor… but when you are working on sockets, touching neutral to earth, or touching neutral with fingers may cause the rcd to trip as it should. It is sensing a fault between neutral and earth.

Mislabelling of consumer units is a common problem and not unique to “working class” homes as you put it.


I’ve seen some pretty upmarket builds with the same problems… it’s like no testing was done afterwards… just bang test and walk away.
Ok so the rcd tripping if i touch neutral and earth even after isolating the circuit is normal. I asked because duckgo AI said it must not happen. After all i am thinking how can electricity reach rcd earth link if there must not be any electricity in the circuit.
But yes rcd serves 3 mcbs.
So the only issue remaining to explain us If i turn off one of the first two mcbs nothing happens and there is electricity in all sockets.
They appear to be 1 linear and two rings.Left to right edge
1000076668.jpg
 
Last edited:
It is perfectly normal I doubt there isn't an electrician it hasn't happened to.
Are you saying two MCBs need to be off to isolate the sockets?
 
It is perfectly normal I doubt there isn't an electrician it hasn't happened to.
Are you saying two MCBs need to be off to isolate the sockets?
Yes thats what i am saying. Turning off the first mcb with one wire does nothing and i cant find anything in the house off. Also turning off the second mcb on a ring does nothing and all sockets works fine on all floors. I actually havent tested only turning off the third one.
Edit: I just turned off third mcb for upper sockets and it turned them off fine but strangely there was a delay of about 30 seconds. I turned off the mcb went upstairs plugged my phone then it said charging for 2 seconds then it went off.
Anyway.
Only after turning off the first two do i not have electricity in the sockets on the ground floor. But after i guess i touch the neutral on the sockets rcd trips off and there is no electricity on all sockets around the house.
Please can you explain how rcd knows that there is a "fault" on a isolated circuit? Does it not need electric impulse to go through the neutral or earth to the rcd? Or is rcd on a battery?
 
Last edited:
Try just turning the third one off, if you get the same result the circuits are interconnected across the MCBs and that needs addressing.
 
Don’t use a charger to check for power at a socket… if you don’t have a proper tester, you could use a table lamp… a charger, lead and phone could give a false reading..


The mix up with the sockets could be that one leg of a ring circuit has been swapped with the single radial circuit.
It needs tested properly by someone with the test equipment required.
 
Don’t use a charger to check for power at a socket… if you don’t have a proper tester, you could use a table lamp… a charger, lead and phone could give a false reading..


The mix up with the sockets could be that one leg of a ring circuit has been swapped with the single radial circuit.
It needs tested properly by someone with the test equipment required.
Ok got it. So it might be as simple as swapping the live wires. I would love to call electritian to do it but as you can see they done the eiring 5 years back.
I will wait for my father who knows this better to come and test ehich wire is where.
Can someone explain how rcd works :)
 
I read and watched this
View: https://m.youtube.com/watch?v=K-ZtRd_OO-I&pp=ygUMSG93IHJjZHdvcmtz

But what i understand is you need pulse in the circuit. I will shut down all three mcbs and work on last socket tomorrow see if the rcd will trip
That's great - perhaps slightly more in-depth than I was thinking of!

An RCD doesn't need a pulse in the circuit, although in the instance of it responding to a person touching a live wire, it will see the sudden imbalance and respond.
The RCD sits there constantly monitoring that the live current matches the neutral current 24 hours a day. There can often be a very slight imbalance, say a milliamp or so, but once that imbalance current gets to somewhere over 15mA (typically 18mA to 25mA) the RCD will trip, irrespective of whether it's a person touching live, some water getting into the wiring, an appliance fault, or a mouse chewing a cable, or some electronic component such as a capacitor going faulty. The change in leakage current can happen gradually over time, until tripping point is reached, when the RCD disconnects the circuit(s), seemingly at random. This is when test equipment can be so useful.

The video takes the rather extreme example of 2A flowing to ground, but an RCD will typically trip at one hundredth of that (to save a life!). So trips can be caused by having a large number of earthed electronic gadgets plugged in (don't necessarily have to be on to be causing a leakage), or an appliance such as an oven or washing machine with some leakage.
 
That's great - perhaps slightly more in-depth than I was thinking of!

An RCD doesn't need a pulse in the circuit, although in the instance of it responding to a person touching a live wire, it will see the sudden imbalance and respond.
The RCD sits there constantly monitoring that the live current matches the neutral current 24 hours a day. There can often be a very slight imbalance, say a milliamp or so, but once that imbalance current gets to somewhere over 15mA (typically 18mA to 25mA) the RCD will trip, irrespective of whether it's a person touching live, some water getting into the wiring, an appliance fault, or a mouse chewing a cable, or some electronic component such as a capacitor going faulty. The change in leakage current can happen gradually over time, until tripping point is reached, when the RCD disconnects the circuit(s), seemingly at random. This is when test equipment can be so useful.

The video takes the rather extreme example of 2A flowing to ground, but an RCD will typically trip at one hundredth of that (to save a life!). So trips can be caused by having a large number of earthed electronic gadgets plugged in (don't necessarily have to be on to be causing a leakage), or an appliance such as an oven or washing machine with some leakage.
Ok fair enough explanation but if i isolate via the mcbs all circuits and only the rcd is on even if i touch say neutral and earth how will RCD know that and trip if no electricity should be in the system?
 
Ok fair enough explanation but if i isolate via the mcbs all circuits and only the rcd is on even if i touch say neutral and earth how will RCD know that and trip if no electricity should be in the system?
Because the Neutral potential in your house is slightly above earth caused by all the other houses around consuming electricity, and the tiny resistance of the supply cable back to the local transformer (where it's earthed, or wherever it is earthed) means there is probably a small voltage between your neutral supply and earth at your consumer unit. So when you short a neutral supplied through the RCD to ground, current flows in that neutral, but there is no corresponding current in the live, so the imbalance trips the RCD.
The voltage that does it is on the neutral. It might also be getting there within your property, fed by leakage and suppressor currents on other circuits (eg with a split CU) that are still on.

If you turn off the double pole mains switch on the CU to isolate the neutral - does it still do it?
 
Last edited:
Don’t use a charger to check for power at a socket… if you don’t have a proper tester, you could use a table lamp… a charger, lead and phone could give a false reading..


The mix up with the sockets could be that one leg of a ring circuit has been swapped with the single radial circuit.
It needs tested properly by someone with the test equipment required.
... And requisite knowledge!
 
Because the Neutral potential in your house is slightly above earth caused by all the other houses around consuming electricity, and the tiny resistance of the supply cable back to the local transformer (where it's earthed, or wherever it is earthed) means there is probably a small voltage between your neutral supply and earth at your consumer unit. So when you short a neutral supplied through the RCD to ground, current flows in that neutral, but there is no corresponding current in the live, so the imbalance trips the RCD.
The voltage that does it is on the neutral. It might also be getting there within your property, fed by leakage and suppressor currents on other circuits (eg with a split CU) that are still on.

If you turn off the double pole mains switch on the CU to isolate the neutral - does it still do it?
Thanks so much that makes sence. I will try it both with just 3 mcbs off and with the all main supply off. Altough i do recall on all other occasions I worked on the electrical things around the house i always had turned off the main mcb and never had to touch the rcds till now. Now I am married.
But will see.
 