Hi all
Was looking in to the adibatic equasion as our company will not let us add on to a Ring circuit with 1mm cpc..
I want to give some evidence as to why it may not be an issue.
My question is;
If the circuit is protected by an rcd can I replace fault current in the adibatic equasion with 30ma as that is all the rcd will potentaly allow to flow down the cpc?
If you have a low resistance fault from phase to earth.
the current that flows will be dependent upon the loop impedance.
if this causes an imbalance through the rcd over 30mA (it should) then the rcd should open to clear the fault.
It will not limit the current that flows as it has no current limiting circuitry inside it other than a trip mechanism to turn off the supply to the load.
Thanks James
So I could replace the 0.1 trip time in the equasion with the actual measured 1x trip time of the rcd ?
Also I'm struggling to know where exactly to take my fault current from. The start of the circuit where fault current will be at it highest. Or just simply from my zs of thay circuit
In general the RCD will only provide better (i.e. lower I2t energy) fault limiting for the region below the MCB "instant trip". So if you have your typical 32A B-curve MCB then it will go in under 20ms for any current above 5*32 = 160A and the speed of disconnection (below a cycle of the supply) provides the energy-limiting aspect.
Below that magnitude of fault current then the MCB can take seconds to trip on the thermal curve, but the RCD for earth-faults will go in tens of milliseconds instead. So while it might stop the CPC slowly roasting at 30-odd amps under very odd fault conditions it is rarely the aspect that will decide on CPC minimum size.
For UK plugs the 13A fuse also serves to limit long-term overload on such faults (e.g. very long extension lead shorted out) but these days the RCD ought to disconnect long before that.
Reply to RCDs for fault protection in adibatic equasion in the UK Electrical Forum area at ElectriciansForums.net
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...