Rf interference with rcd

littlespark

~
Staff member
Esteemed
Arms
Supporter
Patron
I mentioned this on the “smart meter hate” thread, but I thought I’d start a new one.


I’ve read on here about smart meters causing RCDs to trip just from the radio frequency interference or whatever.

I had a customer text me on Saturday saying their heat pump was tripping off every couple of hours, but it only happened since they got a smart meter.
Over the phone, I suggested a biscuit tin…
They scoffed, but tried it… and it held until overnight. They don’t know when, and they didn’t know to reset it.

I changed the plastic box it was in for a metal enclosure, and reused the devices… simply because CEF sent me the wrong stuff.
Overnight, it has tripped again.

I’m going to go back, extend the tails and move the enclosure away from the vicinity of the meter. Will change the rcd from type AC to A and see if that helps.

There is a plastic split board feeding the rest of the house off the right hand side of the photo, with an rcd inside it, but that has never tripped.
That should be far enough.

IMG_1955.png
 
a little bit of an update...

The customer texted to say meter engineer acknowledged the radio meter is indeed tripping the rcd... .and removed the radio hub, and is organising a cellular communications instead... They were going to put me off going back, but they have said its tripped again.

I dont know if "removing the radio hub" is the top half of the meter, or just the receiver and screen that shows the consumption. I'll find out tomorrow.
I will still change the RCD to type A, and move the enclosure away from the meter.

It would be a coincidence if the pump itself developed a fault at the same time as the smart meter was put in.... AND is now tripping less frequently after changing the enclosure to metallic.

The old RCD is possibly weakened through constant cycling on and off several times a day
 