I mentioned this on the “smart meter hate” thread, but I thought I’d start a new one.
I’ve read on here about smart meters causing RCDs to trip just from the radio frequency interference or whatever.
I had a customer text me on Saturday saying their heat pump was tripping off every couple of hours, but it only happened since they got a smart meter.
Over the phone, I suggested a biscuit tin…
They scoffed, but tried it… and it held until overnight. They don’t know when, and they didn’t know to reset it.
I changed the plastic box it was in for a metal enclosure, and reused the devices… simply because CEF sent me the wrong stuff.
Overnight, it has tripped again.
I’m going to go back, extend the tails and move the enclosure away from the vicinity of the meter. Will change the rcd from type AC to A and see if that helps.
There is a plastic split board feeding the rest of the house off the right hand side of the photo, with an rcd inside it, but that has never tripped.
That should be far enough.

I’ve read on here about smart meters causing RCDs to trip just from the radio frequency interference or whatever.
I had a customer text me on Saturday saying their heat pump was tripping off every couple of hours, but it only happened since they got a smart meter.
Over the phone, I suggested a biscuit tin…
They scoffed, but tried it… and it held until overnight. They don’t know when, and they didn’t know to reset it.
I changed the plastic box it was in for a metal enclosure, and reused the devices… simply because CEF sent me the wrong stuff.
Overnight, it has tripped again.
I’m going to go back, extend the tails and move the enclosure away from the vicinity of the meter. Will change the rcd from type AC to A and see if that helps.
There is a plastic split board feeding the rest of the house off the right hand side of the photo, with an rcd inside it, but that has never tripped.
That should be far enough.