No more books.
You could be right there.
I reckon the only two you need are GN3 & 8.
The big green one you can twist it around for everthing you want!
0.74 was a guess i did every test result i had even i did 0.27+0.45/4 and it comes up 0.3825 so i put this result in and i got a fail??
indeed it does lol drinking and maths and 1am dont go well together but the calculator won that argument, ill try it now.
Untitled.png LMAO when i clicked check line - line it clips both blue wires this programme is not good i thinks lol
Sorry to be disheartening but that virtual thingy looks like a load of nonsense.
If your L-L reading is 0.27 ohms (r1), N-N reading is also 0.27 ohms (rn) and your E-E reading is 0.45 ohms (r2) then there is no way on this planet that your R1+R2 reading is 0.74 ohms. Even though this simulator says 0.74 is correct, trust me it's not.
The CORRECT R1 + R2 is 0.18 ohms
If you believe to much in that programme you will fail big style.
my tutor has just confirmed that the senario is indeed wrong and that all you helpful sparkys were right so thanks alot to you all :)