sedgy34
I have just had a similar problem. I went to a customers house to install a double socket into an existing ring but on testing the ring for before carrying out the work I found the was no continuity on the L,N or E. Now ALL the sockets are working and I have identified which leg is feeding these sockets which means it can only be the last return leg back to the board. I explained to the customer what the problem is and the implications it could have but his response was "well its worked ok up until now so just leave it" as he didnt want the mess of me trying solve the issue. I put the circuit on a 20a breaker and told him I was unable to install a new socket until this problem was fixed.
So now you have a radial why didn't you just disconnect a leg out the mcb and instal the socket your customer wanted