Actually this is not the case. See this excerpt from the MyEnergi website:

"It is important to note that the standards for EV charge point installation usually require an RCD which meets a specific standard – IEC 61008 for an RCD or IEC 61009 for an RCBO. The RCD in zappi does not fully meet these requirements which means that a separate RCD or RCBO to these specific standards needs to be installed."
I stand corrected.
This has changed in the last year or so - previously Myenergi stated their RCDs were compliant. I double-checked with them on more than one occasion. (I also checked with NICEIC if a "Type-A + 6mA DC" met the requirements - and they said YES!) :(
 
I stand corrected.
This has changed in the last year or so - previously Myenergi stated their RCDs were compliant. I double-checked with them on more than one occasion. (I also checked with NICEIC if a "Type-A + 6mA DC" met the requirements - and they said YES!) :(
Lot's of us have been similarly burned. Napit said the same.
 