younglearner

Hi all im a young learner so be basic with me aha

I want to wire up my shed at bottom of garden its appdox. 80 metres fuse box to fusebox i have a 40amp fuse
Box in the shed it has a 6a mcb and a 32a mcb i need to connect the two the obvs was 6mm swa however at 230 quid for 100m i was wondering if i could use 6mm T&E through conduit to wire both fusebox together??

Next question

If i was to be able to use 6mm t&e wah size cable in the shed to wire plug sockets and light?? And how many double plug sockets can i have coming off the 32a mcb i was hopibg for four??
 
Prob go for 10mm in conduit for that distance.

1mm for light, 4mm for sockets and loads on a 32a mcb.
 
did some basic calcs, and looking at the regs with a total load of max 2kW you will be fine with 4mm buried swa.
2.9% volt drop.

according to common sense you will be fine with a 2.5mm swa on 20a radial, will be enough for couple of lights and powering your tools, unless you got some big industrial gear in there.
 
Great help cheers but how come not 6mm thought that would be plenty?? #stillearning
 
Oh its more of a boystoys mancave shed so at any one time there wud be turned on kettle tv games console light amp for speakers if this changes anything??
 
have a look on your gear and lights power consumption. add it up together, must be less than 20 amps.
means no kettle and heater together, with games and hifi you will be fine.
 
Looking at what you have specified and from an online cable calculator, you will need no less than 16mm twin and earth cable in conduit (which isnt worth the hassle, better off with SWA). this will give you the 40a required load and account for volt drop.

To answer your question about why not 6.0mm, all cables have resistance and resistance reduces the voltage across its length. at 80m you will have 230v at its starting point but used up far too much voltage just getting to the shed. this is comounded by the high load that you require. in order to get the 40amps and drop only a few volts (therefore still being able to power 230v equipment in the shed) you would need a much bigger cable.

Aint as easy as it seem is it.

Are you trainin gto be a sparks or a DIY'er
 
By Law, this will also be notifiable. If you are part P registered then all good. If not, you will need to get your Local Building Control involved at a cost of around £200-£300, depending on your Council.
You will also need to test it all with calibrated gear, and produce certification.
 
Confused?? Too many different cable sizes flying around lol if 6mm swa is ok to use how come 6mm twin and earth isnt?? in the shed i want 4 double sockets one light coming off the 40a fuse box
 
As Guitarist says, If you try to do this yourself, you will need to pay LABC a silly amount of money to come and inspect the works, not taking into consideration the test gear and calibration fees you will have to pay.

No offense, but you aren't sending us the signs of a competent person by the types of questions you are asking... you should get a qualified and registered electrician in to do the job, it will be a lot less hassle in the long run! If you post where you are, a sparks from the forum might be able to come and have a look... :)
 