Does it happen?.Is it even possible.?.I ask the question because I have never experienced the issue professionally and have become increasingly convinced that with a standard plastic switch it is not even possible.The traditional reasoning behind mounting a light switch outside a bathroom is due to the perception that a credible risk of shock due to dampness/condense exists if it is mounted inside.However I have repeatedly tested the resistance between the live terminal of a switch and the outside of the switch (where a finger would be positioned) while submersing the switch in water and not got a resistance lower than 20,000 ohms.
 
Not to the same extent, but by your reckoning, you wouldn’t need weatherproof switches for outside?

Water creates rust, along with any other impurities can get into the switch and create a path between parts that should be separate.

A lot of times an electric shock is more “shock” than electricity felt by the user. The big bang, a flash of a spark as the current finds the shortest route through moisture.
 
Was that pure water, or one with anything ionic dissolved in it (like salt, etc)? Makes a big difference to conductivity!

The other issue with doing a quick test on a given switch is it will not prove that all makes or models of switch are going to be the same. That is what the standards and/or manufacturer's specifications cover.

Personally I think switches should be inside the bathroom to stop a-holes messing about when someone is in there, but suited to the location (i.e. how close to any likely source of water, if rated for high humidity operations, etc).
 
Water creates rust, along with any other impurities can get into the switch and create a path between parts that should be separate.
This is the point I wanted to address.(prompted by the current thread "Mains electric shock from plastic light switch").Even by creating a direct water path between parts that "should be separate",I still cannot get a resistance lower than 20,000 ohms.And I am erring on the conservative side.I,m not wanting to make an argument here for using plastic switches in bathroom or anywhere else.Its more to be able to electrically analyse potential faults more accurately and to be able to confidently rule out whether dampness is an issue or not.The post I quoted above is from a gentleman who's light switch is not in a bathroom
 
Was that pure water, or one with anything ionic dissolved in it (like salt, etc)? Makes a big difference to conductivity!
Used tap water.I would imagine moisture damp would probably be purer again and have a higher resistance
The other issue with doing a quick test on a given switch is it will not prove that all makes or models of switch are going to be the same. That is what the standards and/or manufacturer's specifications cover.
Valid point.I am referring only to the standard plastic MK or Click type switch with a centimetre gap from live terminal to outside of switch
Personally I think switches should be inside the bathroom to stop a-holes messing about when someone is in there,
Agreed
but suited to the location (i.e. how close to any likely source of water, if rated for high humidity operations, etc).
Agreed.

As an aside I was recently in a holiday home in the north of Sweden.3 mts x 2 Mts.It had a light switch 30 cms from shower.A socket 60 cms from shower.Two other double sockets and the house distribution board all included in the room🙂
 
Does anywhere else in the world have this nonsense attitude regarding switches in bathrooms?

I don't think it's wise to use some of the other foreign electrical systems as a reference - if you start doing that we'd have all sorts of dodgy ideas.

Not saying they're all bad obviously, but there are some distinctly poor practices around
 
Was that pure water, or one with anything ionic dissolved in it (like salt, etc)? Makes a big difference to conductivity!
Used tap water.I would imagine moisture damp would probably be purer again and have a higher resistance

The switch suspected of causing a shock through dampness in the recent thread, had been connected to an energised circuit and is suspected to have been leaking between contacts before the shock (evidenced by the light flashing). If liquid within the switch was passing the leakage current for a time, a significant concentration of ions could have dissolved into it through electroysis of the live metal components. A smear of this liquid escaping over the surface might have created a much more highly conductive path than submersion in clean water, where any solutes would be much more dilute.
 
The switch suspected of causing a shock through dampness in the recent thread, had been connected to an energised circuit and is suspected to have been leaking between contacts before the shock (evidenced by the light flashing). If liquid within the switch was passing the leakage current for a time, a significant concentration of ions could have dissolved into it through electroysis of the live metal components. A smear of this liquid escaping over the surface might have created a much more highly conductive path than submersion in clean water, where any solutes would be much more dilute.
 
The switch suspected of causing a shock through dampness in the recent thread,
According to the OP from post 26

"There was no sign of moisture inside the switch found by me or the electrician"

"I have never seen any other signs of damp or water leaks "

had been connected to an energised circuit and is suspected to have been leaking between contacts before the shock (evidenced by the light flashing). If liquid within the switch was passing the leakage current for a time, a significant concentration of ions could have dissolved into it through electroysis of the live metal components. A smear of this liquid escaping over the surface might have created a much more highly conductive path than submersion in clean water, where any solutes would be much more dilute.
Agree with all the above.But until evidence for moisture been present is established it remains speculation.I think checking his earthing remains the most practical next step.
 
Apologies for digging up a 9 month old thread, but was going to post about a fault-finding job I did today where I can confirm that it is possible to get a shock off the plastic bit of a plastic switch, and this seemed as good a place as any to put it.

Client reported getting a shock off the switch after cleaning it (getting rid of mould nearby), and also that the landing light (LED GLS) was glowing dimly when off (normal brightness when on). House is COLD - really cold, can see your breath cold - elderly resident cannot afford to put the heating on (and no heating in the 3 foot square hallway anyway). Switch is 2G in hall: 2-way for landing, and 1-way for hall lights. No L link wire between hall and landing switches - on the face of it, separate. 2x lighting circuits, neither RCD-protected. Client had turned off both lighting circuits at the DB.

Checked:
  • Zs@DB fine (0.20Ω), TN-C-S, incoming polarity good
  • Bonding good
  • R2 to switch back box/lugs: 0.10Ω (to MET)
  • Confirmed polarity on switches
  • Confirmed earth continuity to upstairs switch (for and on the landing).
  • No cpc at landing light, pendant set, loft boarded above.
  • IR (L+N) to E for upstairs and downstairs circuits in parallel 1.06MΩ but a little variable
  • IR upstairs N to downstairs N 3.39MΩ
However:
- Continuity upstairs L to downstairs L ~33kΩ

~scratches head~

So upstairs and downstairs lighting circuits are linked "somehow" possibly via a lamp...? Resolve to put both up and down L on one MCB (2 circuits to 1). Having confirmed earthing, polarity, IR, and joined two circuits together (which were "somehow" linked) I restored power to the circuit(s).... and got a shock off the plastic bit of the switch.

  • Voltage MET to pattress screws: <10V
  • Voltage MET to the plastic bit of the switch: ~ 34V
  • landing light glowing dimly

Ah! So downstairs permanent L is tracking across the 2G switch to the upstairs switched L. Gotcha.

Power off, chuck the 2G switch in the bin. New 2G plastic switch...:
  • IR upstairs L to downstairs L: now >10MΩ
  • Back to 2 separate circuits
  • No more tingly tingly, landing light now turns properly off.

So yes, shock off a plastic switch is apparently a thing. Marvellous.
 
Apologies for digging up a 9 month old thread, but was going to post about a fault-finding job I did today where I can confirm that it is possible to get a shock off the plastic bit of a plastic switch, and this seemed as good a place as any to put it.

Client reported getting a shock off the switch after cleaning it (getting rid of mould nearby), and also that the landing light (LED GLS) was glowing dimly when off (normal brightness when on). House is COLD - really cold, can see your breath cold - elderly resident cannot afford to put the heating on (and no heating in the 3 foot square hallway anyway). Switch is 2G in hall: 2-way for landing, and 1-way for hall lights. No L link wire between hall and landing switches - on the face of it, separate. 2x lighting circuits, neither RCD-protected. Client had turned off both lighting circuits at the DB.

Checked:
  • Zs@DB fine (0.20Ω), TN-C-S, incoming polarity good
  • Bonding good
  • R2 to switch back box/lugs: 0.10Ω (to MET)
  • Confirmed polarity on switches
  • Confirmed earth continuity to upstairs switch (for and on the landing).
  • No cpc at landing light, pendant set, loft boarded above.
  • IR (L+N) to E for upstairs and downstairs circuits in parallel 1.06MΩ but a little variable
  • IR upstairs N to downstairs N 3.39MΩ
However:
- Continuity upstairs L to downstairs L ~33kΩ

~scratches head~

So upstairs and downstairs lighting circuits are linked "somehow" possibly via a lamp...? Resolve to put both up and down L on one MCB (2 circuits to 1). Having confirmed earthing, polarity, IR, and joined two circuits together (which were "somehow" linked) I restored power to the circuit(s).... and got a shock off the plastic bit of the switch.

  • Voltage MET to pattress screws: <10V
  • Voltage MET to the plastic bit of the switch: ~ 34V
  • landing light glowing dimly

Ah! So downstairs permanent L is tracking across the 2G switch to the upstairs switched L. Gotcha.

Power off, chuck the 2G switch in the bin. New 2G plastic switch...:
  • IR upstairs L to downstairs L: now >10MΩ
  • Back to 2 separate circuits
  • No more tingly tingly, landing light now turns properly off.

So yes, shock off a plastic switch is apparently a thing. Marvellous.

What brand was the switch, and how old was it?
 
That's a Crabtree 2172, and the 2000 series were known to be susceptible to 'shocking' in a damp atmosphere. Crabtree virtually admitted to this when they emphasised the improved resistance to water entry in the publicity blurb, when the 4000 series was introduced.
Fantastic! Thanks for the information, that's superb!

It's all coming out now.... :)
 
That's a Crabtree 2172, and the 2000 series were known to be susceptible to 'shocking' in a damp atmosphere. Crabtree virtually admitted to this when they emphasised the improved resistance to water entry in the publicity blurb, when the 4000 series was introduced.
Very interesting.I would add that ,since plastic is technically a non-conductor of electricity, would it be more correct to describe these Crabtree makes as "non-plastic"? They must have contained a component or additive that allowed for conduction.
 
Very interesting.I would add that ,since plastic is technically a non-conductor of electricity, would it be more correct to describe these Crabtree makes as "non-plastic"? They must have contained a component or additive that allowed for conduction.

Could be poor quality or contaminated plastic maybe. I've seen that happen in a production environment where the plastic body of a batch of mains inlet sockets failed, although admittedly that was during 3kv flash tests.
 
Water isn't technically a conductor either, but we all know that in most cases it is and this was the problem with 2000 series switches. There was a small and fairly short route between the plastic of the switch body and the plastic of the rocker, all the way into the live contacts. This drew water in by capillary action, causing the rocker to bite whoever touched it. Once dried out, they were fine again.
The promotional stuff when the 4000 series was introduced, referred to 'increased labyrinth design' or something like that, around the rocker.
 

Reply to Shock from switch due to dampness in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all! This is my first post and I have registered to ask for some help with troubleshooting an electric shock I got from a plastic light switch...
Replies
44
Views
8K
Considering upgrading to pull-cord or water resistant wall switch. Heard those European style switches are safer due to different design (better...
Replies
37
Views
9K
Squid
S
Someone asked about abbreviations used here. So I tried to copy a list I made elsewhere: A/C Air Conditioning AC Alternating Current ACB...
Replies
41
Views
5K
Please help, I'm still new to testing for myself and sometimes I wonder if my new Megger is being naughty on purpose as my Fluke wasn't as prone...
Replies
27
Views
5K
J
Hi Folks, Bit of an introduction thread - I'm a total newbie on this forum and looking for a bit of advice. Just moved in with my gf for the...
Replies
14
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock