ipf

~
Mentor
Arms
Seen one this aft. Council Grant job. Asked to isolate upstairs shower prior to removal and replacement. Wylex 6way cu (3036) plus extra 1way cu (45amp 1361). Outgoing cables include one 10mm and one 6.0mm (t+e's). Hob and oven in kitchen. Isolated shower(6.0mm) at 1way unit and decided to check kitchen. Found hob also isolated. 9.6 shower and electric hob. Under the landing floorboards, the 6.0mm cable had been cut and jointed using 30amp chocs with a bit of tape. The homeowner contacted the installer, a 'fully qualified' son of a friend, who admitted the installation but denied the connection? Ongoing.
Points. Never presume... who sorts out the c**p?... and who pays for it?
 
The jerk just phoned. I asked him for his thoughts on 'fire hazzards'. He laughed down the phone. I hung up.