Advice please
In a wet room 1m wide 2.2m long containing electric shower at one end, can the pull switch be fitted at the opposite end which is outside any zone ? and dose the switch have to be IP 44
With thanks in advance
 
Zone 0 = at least IPX7.
Zones 1 = and 2 at least IPX4.
Exposed to jets of water = IPX5.
Outside zones = suitable for purpose and environment.
 
Last edited by a moderator:
Don't forget that providing you have sufficient height above 2.25m from the finished floor level and the ceiling that this space is outside the zones and may be used to mount a pull cord isolator with the cord hanging inside a zone if necessary.
 