It's been years since I've fitted a dual RCD board, RCBOs all the way now. I also went to a new build recently and the certificate for the property didn't match the installation at all. Though that was the least of the problems with the wiring.
I’m going to get the builders to arrange another company to do an EICR
 
I Dont fit Hager boards but is that SPD even wired up? Usually when the SPD sits to the right of the main switch its fed from an MCB, how does the bus bar get from the main switch to the SPD past the neutral terminal on the switch if its fed direct.

Edit: I've just found this picture which explains it,

maxresdefault.jpg


dont really like that, how thick is the fly-lead and what happens if the SPD shorts live to neutral, that cable will fry before the main fuse goes but I suppose the neutral lead would do the same on other SPD's fed direct from the bus bar. Wouldn't surprise me if SPD's end up causing a whole load more problems than they solve in the coming years.
 
I Dont fit Hager boards but is that SPD even wired up? Usually when the SPD sits to the right of the main switch its fed from an MCB, how does the bus bar get from the main switch to the SPD past the neutral terminal on the switch if its fed direct.

Edit: I've just found this picture which explains it,

maxresdefault.jpg


dont really like that, how thick is the fly-lead and what happens if the SPD shorts live to neutral, that cable will fry before the main fuse goes but I suppose the neutral lead would do the same on other SPD's fed direct from the bus bar. Wouldn't surprise me if SPD's end up causing a whole load more problems than they solve in the coming years.
I’ve not even had the time to remove the board cover at the moment still busy trying to sort out everything else wrong with the build! Will post a picture tonight when I’m home 😂
 
  • Like
Reactions: freddo

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Adam_92

Trainee
~
Joined
Location
luton
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Snagging on a new build
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
Adam_92,
Last reply from
Adam_92,
Replies
22
Views
1,659

Advert