hi there
all the connections the builder made are now either under concrete or inside a brick wall.
the fuse board is relatively new and definitely has no doorbell specific trip switches... I think its a transformer i need to find?

tx
Mark

Oh deary me not much chance off checking them then, Sodding builders
 
There are various possibilities for the failure for your doorbell, the spring could have become tired or broken and need replacing, you have high resistance connections in your supply cable / switch transformer supply cable. Your cables are too thin to carry the required current, your transformer is now too far from your bell to supply the required voltage, the volt drop from the bell push is reducing the voltage in the same way.

A standard bell transformer is not adjustable, they tend to be 12V supplies. The capability to supply current is different for different transformers.

If the transformer is not man enough then it will be slightly difficult for you to get a more powerful replacement as they are not standard items.

A bell transformer could look like any of the attached pictures.
Old bell transformers were generally placed either near the bell unit or near the consumer unit. Occasionally they would be in the roof space above the door or in the attic.New bell transformers can be fitted into the consumer unit, you could also have a transformer looking like a laptop power supply, but much less likely.
DBell TX1.jpgDBell TX2.jpgDBell TX3.jpgDBell TX4.jpgDBell TX5.jpg
The builder should not have covered the connections for the door bell as they should always be accessible (unless they were permanently fixed, so it may be worth looking again.
 