Ive been asked to run supply for a 8.5kw shower. Originally i thought i would run a 10mm.

Did the 8500/230 and got 36 amps. So would i be ok to run 6mm instead?

The cable will be enclosed in trunking by itself and the run is about 14mtrs.

Your advise is much appreciated

ps what is this > :93:
 
6mm cable in conduit on surface of wall = 38A

For the conduit
Cable has a factor of 58
58x6m
=348
Meaning you need to use 25mm conduit (Cable factor of 487 & <) if you are going in straight lines
If you have bends use 25mm for 1 bend and 32mm for 2 beds

Get yourself a copy of Advanced Electrical Installation Work (ISBN = 978-0-7506-8752-2)

Cable sizes, RCDs and MCBs from Page 277
 
Last edited by a moderator:
i would stick with 10.0mm as this allows for future upgrades/changes to 9.5kw etc.

if there isn't a scale filter on the water feed then it WILL need changing pretty soon.
 
6mm cable in mini trunking is adequate for an 8.5kW shower. no insulation derating. seems some members have been brainwashed into suggesting 10mm cable for anything above 30A.
 