did start with that but you could not get any consistency as it had seemed to hold when 3 mcbs were off at the end of the sub but would hold and fail with no consistency at all,Can you knock off all the circuits on the end of each sub and then energiser them one by one ? I would have the neutrals out as well !
Granted... with a touch of tracing stuff out to find the possible borrowed neutral tripping the other rcdThis is looking like a strip down of the sub boards here, neutrals out and reconnect one at a time until she pops,
only in blue plastic,Are there any metal water pipes or anything like that linking the two sites in any way ?
Could be worth a try, nothing venturedWhat about IR testining between neutral bars to see if it is the neutral!
Hi A1guvner , did you ever get to the bottom of the fault ?