Source for Type B, 40A 30mA C-curve 2M RCBO

I'm replacing the RCBO in an elderly Rolec wallpod. The original Rolec ACEQ0185 Type A device started randomly tripping after a few years so I replaced it with a Type A Garo GRC40. The Garo was fine for 4 years but now is random tripping. It seems sensible to replace it with a Type B device but I can't find anything that's 2-modules wide that will do the job. I'd welcome suggestions. (If necessary I'll fit a 1M device, but would prefer not to have to do this)
 
Is there an RCD protecting the circuit TO the wallpod? It might be that you dont need it in the wallpod itself

The other point is, that the RCD may be tripping purposefully because there is a fault, not because IT is faulty.
Have you had it checked?
 
The "pod" is fed from an MCB (of course) and, because of EV characteristics and possible failure mechanisms, the RCBO needs to be either Type A or B - Type B being preferred because of the DC "blinding" risk with Type A.

The existing RCBO trips randomly (but infrequently) with/without one of two cars plugged-in, and on dry or wet days. There is no measurable leakage so I think it's fair to assume that it's an RCBO problem or, possibly, something odd happening on the supply. It's a TN-C-S system but, because of the overhead 2-wire feed to the house, I've added an additional earth rod. Without hiring a data logger to leave on until the next trip (which may be weeks away) I don't see how I can diagnose further. It's simpler and cheaper to change the RCBO - hence the request for suggestions for a suitable device.
 
... and finally, in case it's of interest to someone in the future, I've realised that "littlespark" was correct that I don't need an MCB in the EVSE as the one in the CU will do the job - this allowed me to look for MCCBs (rather than RCBOs) and found that Tongou have a Type B RCCB at a good price and which is well reviewed - one is winging it's way to me as I type this.
 