Sourcing a Distribution Board?

Hi, I am trying to source a 6 way 3phase (B form layout) with an 4 pole RCCB 100A 30mA incomer, it's to be installed on TT system hence the the incomer. Not too concerned about SPDs just yet, as a risk asessement of the install returns negligeable risk to equipment.
Had quotes from major brands but the costs are too great when MCBs and RCBOs are included. I am reluctant to say it but a Chinese brand would suffice.
Any suggestions of Brand and supplier would be much appreciated.

thanks Griffey
 
Why do you want a 30ma RCD main switch?
I can't see the reason for one all it does is protects the busbars which are shrouded and almost never likely to cause a fault.
 
You have quotes from brands and not wholesalers?
Hi, Yes I have had quotes from wholesalers for the major brands but they are too expensive e.g Group schnieder and Hager. I need an RCCB incomer to protect all the outgoing 3 phase loads, as the earth rod resistance is app 25 ohms.
Thanks Griffey
 
Hi, Yes I have had quotes from wholesalers for the major brands but they are too expensive e.g Group schnieder and Hager. I need an RCCB incomer to protect all the outgoing 3 phase loads, as the earth rod resistance is app 25 ohms.
Thanks Griffey
If you have a 30ma main switch RCD you will lose all selectivity. The outgoing loads will be protected by individual RCBOs it isn't necessary and will cost 3× as must as a standard switch.
 
If you have a 30ma main switch RCD you will lose all selectivity. The outgoing loads will be protected by individual RCBOs it isn't necessary and will cost 3× as must as a standard switch.
Hi, Thanks for the reply, but I have just looked the prices for 3 pole RCBOs, even the Fusebox brand are £80 each x 6 adds up to quit a bit of money. Surely a single device would be cheaper. Not too worried about selectivity as the premises can tolerate the whole board disconnecting under an earth fault condition.
 
Hi, Thanks for the reply, but I have just looked the prices for 3 pole RCBOs, even the Fusebox brand are £80 each x 6 adds up to quit a bit of money. Surely a single device would be cheaper. Not too worried about selectivity as the premises can tolerate the whole board disconnecting under an earth fault condition.
That isn't really the way forward you should endeavour to install a compliant installation and it costs what it costs. I presume this isn't your money.
So this is six three phase circuits?
 
If it's a client quibbling aboutbthe cost, then set out the options in writing and include why a single incomer RCD is a bad idea. Get them to state in writing that they accept a sub-optimal install if they really want that.
It's called C.Y.A.
 