Hello, I'm hoping for some advice.
We had an EV charger installed at our office last year (3 phase supply, solar PV on roof). New circuit to the rear of the building and standalone from the existing EV charger at the front of the unit.
After installation, it took almost 5 months to recieve the installation certificate (after much prompting).
I had already realised that an SPD was not fitted but I wanted to wait until the certificate arrived before I broached the subject - the quote had stated that the installation would be to BS7671 but did not mention the exact components or optional extras.
The companies response was:
'Under BS 7671, the need for an SPD is based on a risk assessment, and for this installation it was determined that SPD protection wasn’t a mandatory requirement.
So everything has been completed in line with both the agreed works and current regulations.
That said, if you’d like to have an SPD added for extra protection and peace of mind, we’d be more than happy to arrange this and provide a quotation id recommend this to be installed at source to cover the whole building not just the charger.'
I asked if we could have a copy of the risk assessment for our record, but we have gone back to radio silence.
My understanding (probably wrong!) is that an SPD is required unless the customer opts out (we did not), or a formal Risk Assessment has been conducted. Should such an assessment have been provided with the installation certificate?
If we had been asked at the time we would have paid extra for an SPD given that we already have a PV system and the high value of the vehicles being plugged in.
We had an EV charger installed at our office last year (3 phase supply, solar PV on roof). New circuit to the rear of the building and standalone from the existing EV charger at the front of the unit.
After installation, it took almost 5 months to recieve the installation certificate (after much prompting).
I had already realised that an SPD was not fitted but I wanted to wait until the certificate arrived before I broached the subject - the quote had stated that the installation would be to BS7671 but did not mention the exact components or optional extras.
The companies response was:
'Under BS 7671, the need for an SPD is based on a risk assessment, and for this installation it was determined that SPD protection wasn’t a mandatory requirement.
So everything has been completed in line with both the agreed works and current regulations.
That said, if you’d like to have an SPD added for extra protection and peace of mind, we’d be more than happy to arrange this and provide a quotation id recommend this to be installed at source to cover the whole building not just the charger.'
I asked if we could have a copy of the risk assessment for our record, but we have gone back to radio silence.
My understanding (probably wrong!) is that an SPD is required unless the customer opts out (we did not), or a formal Risk Assessment has been conducted. Should such an assessment have been provided with the installation certificate?
If we had been asked at the time we would have paid extra for an SPD given that we already have a PV system and the high value of the vehicles being plugged in.