SPD for EV charger

Hello, I'm hoping for some advice.

We had an EV charger installed at our office last year (3 phase supply, solar PV on roof). New circuit to the rear of the building and standalone from the existing EV charger at the front of the unit.

After installation, it took almost 5 months to recieve the installation certificate (after much prompting).

I had already realised that an SPD was not fitted but I wanted to wait until the certificate arrived before I broached the subject - the quote had stated that the installation would be to BS7671 but did not mention the exact components or optional extras.


The companies response was:

'Under BS 7671, the need for an SPD is based on a risk assessment, and for this installation it was determined that SPD protection wasn’t a mandatory requirement.

So everything has been completed in line with both the agreed works and current regulations.

That said, if you’d like to have an SPD added for extra protection and peace of mind, we’d be more than happy to arrange this and provide a quotation id recommend this to be installed at source to cover the whole building not just the charger.'


I asked if we could have a copy of the risk assessment for our record, but we have gone back to radio silence.

My understanding (probably wrong!) is that an SPD is required unless the customer opts out (we did not), or a formal Risk Assessment has been conducted. Should such an assessment have been provided with the installation certificate?

If we had been asked at the time we would have paid extra for an SPD given that we already have a PV system and the high value of the vehicles being plugged in.
 
You the customer should decide whether you opt out the fitting of an SPD. I would be having a look at the manufacturer's instructions it may well suggest one is required.
 
You the customer should decide whether you opt out the fitting of an SPD. I would be having a look at the manufacturer's instructions it may well suggest one is required.

Unfortunately we were not given any manuals with the installation. There is just a QR code on the wallbox to allow our employees to charge.

Unfortunately I cannot download the manual from Rolec due to our (annoying) IT security policies, although I have contacted them with the same question.

As I understand it from a few hours of Googleing, the 2022 ammentment to the wiring regulations (section 443) removed the option of a risk assessment via calculation, so I think the information our electrician provided is incorrect.

Regulation 443.4.1
Protection against transient overvoltages shall be provided where the consequence caused by overvoltage could:

. Result in serious injury to, or loss of human life, or
. Result in failure of a safety service, as defined in part 2, or
. Result in significant financial loss or data loss

For all other cases SPDs shall be fitted to protect against transient overvoltages, unless the owner of the installation declines such protection and wishes to accept the risk of damage to both wiring and equipment as tolerable.


I would say that bullet point 3 certainly applies to us given the value of the vehicles being connected, let alone any safety issue. We also have a PV system on the building (which doesn't seem to have been notified on the installation certificate) which as I understand it raises the risk.

We certainly did not opt out of having an SPD - it wasn't even mentioned.


I'm hoping that an electrician can confirm if I my understanding of the latest ammendments are correct before I go back to the installer. I'd rather resolve this amicably if possible, but given the difficulties we have had so far, I'm not hopeful.
 
I spoke to Rolec today. Although they recommend an SPD, it is not a requirement in their installation instructions.

So my fall back is BS7671.
 