just been handed this to fit to a TPN DB,have you seen anything so ridiculous,it’s a SPD, those cables are so short,
 

Attachments

  • ABCF42A3-7DDD-4881-8F67-BD5D3DFA518F.jpeg
    94.2 KB · Views: 27
I think they are supposed to be mounted on the side of the DB, closest to the main switch, via a high current breaker (32A or more D-curve, etc) or in some cases just joining blocks. Not sure if there are any punch-out holes or you are expected to drill something.

The short cables are needed to keep the inductance down as lighting surges are only tens of microseconds long and so L usually dominates of R in most cases. A quick look in the 18th regs has max 1m but preferred less than 0.5m total wiring, so 2 * 25cm to the SPD.

Same reason for going for a MCB with a high magnetic trip point - less of a coil for that so lower series inductance.
 
As above, it's designed to fit onto the side of the DB.
 
just been handed this to fit to a TPN DB,have you seen anything so ridiculous,it’s a SPD, those cables are so short,

Yes, the cables must be kept as short as possible, if you make them much longer than that then the SPD won't work properly.

Those cables will be exactly the right length to fit the device where the manufacturer specifies that it goes.
 
Cheers,this is an add on to existing Tpn,where it’s impossible to mount with those connections,to the side of the TPN.
Bearing in mind the max distances,possible to connect @ 1m max with 16mm ,mcb rated @ 63 amp.
 
Cheers,this is an add on to existing Tpn,where it’s impossible to mount with those connections,to the side of the TPN.
Bearing in mind the max distances,possible to connect @ 1m max with 16mm ,mcb rated @ 63 amp.

You'll need to speak to Eaton technical support, only they can tell you what is acceptable for their SPD.
 

Reply to Spd on Eaton Tpn in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
805
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
836
Just a quickie the new amendment certs now have tick boxes for the SPD… would you still add it to the schedule list for the DB… ie: At the top of...
Replies
2
Views
1K
Following the tragic tale from @telectrix about lightning damage to phones and modem leading to a serious loss of beer money I decided to take a...
Replies
0
Views
772
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock