Have a board change to do on a 5 bed house which has had several DIY additions over the years for example has kitchen sockets supplied from 3 different fuses on the existing rewireable board, however all of my IR and continuity tests are acceptable problem is 80% of the sockets are on the original ring main which covers up & down including some in the kitchen, the question is should I be looking at separating the ring into 3 separate circuits? (up,down&kitchen)The house has had lots of alterations including stud walls built over floor board runs which would make it difficult to gain access to the ring and separate it, plus the owner would prefer not to have all her carpets pulled up while I try and find a suitable place to seperate, or am I missing an easy option to split the ring into individual circuits?

Any thoughts welcome!
 
Your remit is to change the CU and to be honest that is as far as it goes, unless the customer wants you to then carry out work on the installation and pay you accordingly.

When you say the kitchen sockets are supplied from 3 different fuses are you say an individual socket as 2 sources of supply, or are there 3 separate socket circuits?

If this 80% ring can be split up into 3 individual circuits at the CU then yes go ahead and do that, but I would bet that is doubtful. My guess would be you would need to delve into this rats nest to do that.

My advice is to change the CU, make the installation safe and do as much as you can at the CU, then on your certification in the part for existing installation include your findings and comments. When you present your invoice, certification etc include a cover letter informing the customer at what you found, what would be your course of action, and assuring them that you are available for advice and able to carry out the remedial work.

They may not want to do this now, but it will prove to them your honest and capable, and that any future work you would have a head start over others
 
My advice is to change the CU, make the installation safe and do as much as you can at the CU, then on your certification in the part for existing installation include your findings and comments. When you present your invoice, certification etc include a cover letter informing the customer at what you found, what would be your course of action, and assuring them that you are available for advice and able to carry out the remedial work.

That is about as good a piece of advice as you're likely to see regarding electrical work.
 
Thanks for the replies,

Malcolm, the kitchen has 4 dble sockets on the main ring and 2 on a dedicated radial and 2 more which are part of a ring that includes an extension at the front of the house which was done about 15 years ago, I will do exactly as you have suggested.

Thanks
 
When you look at a house and it appears to have been extended, always expect the unexpected when it comes to the electrics!
 