H
howdri
was wondering how many spot lights i can put on 1 10 amp mcb if anyone can give me advice please
There would be no de-rating of the mcb but the cable selection would be subject to an number of derating factors such as running through thermal insulation, ambient temperature etc. It may be that to load the mcb to near capacity your circuit conductors will need to be in excess of 1.5mm.