Is there a regulation that says how far from an intruder alarm panel you can install a mains un switched fused spur unit and then subsequently connect with .75 flex?

Cheers in advance.

Dave
 
generally, FCU should be within reach of the alarm panel. guidelines are within 1 meter, but not sure of any specific regulation.
 
BS4737 Unswitched fused spur should be fitted adjacent to control, allowing disconnection for service and repair.
Ok does not state distances....but I would take the word adjacent, meaning next to...
 
Without trawling through the book, I would think just be sensible, I doubt anyone would complain as to the distance so long as its sensible, not too far and obvious as to what it does, I personally would probably stick to 1 meter at the most, its a bit iffy beyond that, I guess so long as its safe and complies, its only a fused spur, I don't see why it cannot be further away, look at it like an outside flood light, fused spur on the wall inside and several meters of cable outside possibly to the light fitting, not directly next to it... just be sensible. As tazz says, "adjacent" meaning "very near, next to or touching". I suppose does it matter if it has the load cable coming out of the front of the faceplate or to the rear.
 
What if the alarm panel is "adjacent" to the CU and has it's own dedicated rcbo in the CU?
 
acceptable, but why a RCBO? i'd stick it on a MCB.
 
tight arse. are you sure you're not a yorkshireman.
 
Had this conversation years ago....and a nice man at BSI, he state, the reason for fused spurs is to allow non qualified electricians, such as alarm installers, to be able to isolate their equipment for servicing or replacement. And the installation of the fused spur, and its wiring from the cpu, should only be carried out by a qualified electrician.
 
BS4737 Unswitched fused spur should be fitted adjacent to control, allowing disconnection for service and repair.
Ok does not state distances....but I would take the word adjacent, meaning next to...

Thanks for all your help guys, I thought that but wanted to be on solid ground.

BTW Tazz BS4737 went out a few years ago. We are on European EN50131 now :)

cheers.. Dave
 