Spur off a spur in 2.5 T&E off a 32A ring circuit in a utility room running a washing machine & a tumble drier. This was reported on a recent PIR of a rental property and the landlord would like it corrected,

The problem I have is if I install a FCU then the customer can only use 1 appliance at a time (apparently not an option in a busy household!!).

So my solution would be to fuse the spur with a 20A mcb in a small 2 module enclosure, which will protect the 2.5 T&E from overload and still allow use of both appliances at the same time.

Can anybody see a problem with this?

I know its not the norm but to incorporate the utility room into the ring circuit will require ripping up a tiled bathroom floor, which the landlord is very keen to avoid.
 
could you not run a leg below the utility room ceiling ( safe zone) or mini trunking and extend the ring?
 
I could but the spur is off the upstairs ring and this will require removal of the tiled bathroom floor for access which the landlord wants to avoid.
 
Done the 20 amp mcb trick myself, can see no problem. In theory if you have 2 single sockets spured from the ring is this different to 1 x twin? But as you know the load may exceed the 20A for a 2.5 best play it safe. As a thought you could limit one of the washing machine socket with a spur if you knew the load. If less than 7 amp 13 + 7 = .... erm 20? Will look tidier if done in a dual box and labelled 'MAX 7AMP' than a small DB.
 
OK , so your solution seems the only way. can't see anything wrong there, only that if 2 machines are on the heating cycle at the same time, they could trip the 20A MCB.or you could sell them a washer/tumbler combined.
 
Not the ring imbalance monster again!!!!!

If 2.5mm2 T&E is rated at 27A (clipped direct) then how can a 20A fused spur overload either leg of the ring?

As mentioned in post 3 it is spured off the upstairs ring which is usually very lightly loaded.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Preston, Lancashire

Thread Information

Title
Spur problem?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
ste mac,
Last reply from
ste mac,
Replies
7
Views
2,079

Advert

Back
Top