L Lighting ~ Mar 25, 2012 #1 Hi all is this ok to run two sfcu like this ? Or should i run it like this
M malcolmsanford Mar 25, 2012 #3 engaged mouth before brain .......................there Last edited by a moderator: Mar 25, 2012
M mickys86 Mar 25, 2012 #6 Haha all the different answers..... Goes back in the arms to see Malcolm's other thread
M mickys86 Mar 25, 2012 #7 GT1 said: No need to run it 2.5... 1.5 will do Click to expand... Obviously 2.5mm from the socket to spur. 1.5 after the spur should be fine but if ya got the 2.5 handy...... I very rarely have 1.5 in the van
GT1 said: No need to run it 2.5... 1.5 will do Click to expand... Obviously 2.5mm from the socket to spur. 1.5 after the spur should be fine but if ya got the 2.5 handy...... I very rarely have 1.5 in the van
S Snapester Mar 25, 2012 #9 Appendix 15 in Green Book shows no issues? Why do you need the 13a FCU at the beginning if the switches are FCU's with 3amp fuses in?
Appendix 15 in Green Book shows no issues? Why do you need the 13a FCU at the beginning if the switches are FCU's with 3amp fuses in?
M mickys86 Mar 25, 2012 #10 TaffyDuck said: See OSG 1st one isn`t fine. Click to expand... You got a page number to look at?
E ezzzekiel Mar 25, 2012 #12 Sigh, yes either one is fine really but first option probably the best no need for fusing down to 13a first if your fusing down to 3a
Sigh, yes either one is fine really but first option probably the best no need for fusing down to 13a first if your fusing down to 3a
E ezzzekiel Mar 25, 2012 #13 TaffyDuck said: See OSG 1st one isn`t fine. Click to expand... In wich case can you give us an explanation as to why not, I'll be very interested in your reasoning
TaffyDuck said: See OSG 1st one isn`t fine. Click to expand... In wich case can you give us an explanation as to why not, I'll be very interested in your reasoning
T TaffyDuck Mar 25, 2012 #14 ezzzekiel said: In wich case can you give us an explanation as to why not, I'll be very interested in your reasoning Click to expand... Admitedly I`m assuming the socket it on a ring as apposed to a spur from a radial Well its a spur, and unfused at its source, therefore as i understand it. OSG Page 68 (7.2.2) " A non-fused spur feeds only one twin socket outlet or one permanently connected item of electrical equipment" Last edited by a moderator: Mar 25, 2012
ezzzekiel said: In wich case can you give us an explanation as to why not, I'll be very interested in your reasoning Click to expand... Admitedly I`m assuming the socket it on a ring as apposed to a spur from a radial Well its a spur, and unfused at its source, therefore as i understand it. OSG Page 68 (7.2.2) " A non-fused spur feeds only one twin socket outlet or one permanently connected item of electrical equipment"
M mickys86 Mar 25, 2012 #15 Yea but it's fused with the 3a sfu?? Maybe you should look at the pics again. Neither picture is showing a spur that isn't fused Last edited by a moderator: Mar 25, 2012
Yea but it's fused with the 3a sfu?? Maybe you should look at the pics again. Neither picture is showing a spur that isn't fused