Ok, the part of the diagram on page 425 shows a spur off the ring main at 9 oclock. The 13A FCU is limiting the current that can flow through to 13A therefore protecting the cable. The OP diagram 1 shows a spur going straight to the first FCU and then on to another FCU. Therefore with 13A fuses put in each it is possible that the total draw could be 26 Amps thus overloading the cable. The 3 amp fuses fitted to the FCU`s are irrelevant as they are protecting the cable going out from the FCU to the appliance.
Now I appreciate that 6 amps, or the load from a boiler and a light (which is going to be less in all likleyhood) is not going to damage the supply cable however the light and the boiler are " fixed equipment" therefore the relevant part of the diagram is at 6 oclock where only 1 fixed item is allowed.
The reasoning for this reg IMHO is that should the fixed equipment be changed in the future, say an immersion for a boiler and a socket for the FCU running the light then you have an overloaded cable.
I refer to my previous post regarding fixed equipment on spurs.