D

DonaldJ

Evening all,

Not too good at being brief but I'll try my best.

CU with 4 ways. One for ring final, one for cooker, one for immersion (which no longer exists so this is now a radial and incorporates the boiler) and one for lights (both upstairs and down).

Spur from the lighting circuit 5a breaker in 1.5mm for about a foot then connected with terminal block to 6mm cable feeding a single socket. This obviously needs to be changed.

Spur from ring final 30a breaker in 2.5mm cable feeding three sockets and a further light under the stairs, not connected via a fused spur.

Spur from 40a breaker in 2.5mm cable feeding 6 sockets in the conservatory.

Truly bizarre.

Question is, how many spurs can you have off a single MCB? I'm thinking it wuold be much better to change the cable feeding the single socket to 2.5mm and moving to the 30a MCB and then taking the current spur connected to the 30a MCB from this single socket. There would be a 13a fused connection between breaker and the first socket on the run.

For the conservatory spur (well, radia really!) I was thinking of also adding this to the ring final MCB, again with a FCU between MCB and the first socket.

How does this sound as a temporary until the CU can be changed? Are you allowed two spurs from one MCB? It's the safest option I can think of for now.

The entire installation is protected by a 30ma RCD between meter and CU.

Cheers folks

Don.
 
Evening all,

Not too good at being brief but I'll try my best.

CU with 4 ways. One for ring final, one for cooker, one for immersion (which no longer exists so this is now a radial and incorporates the boiler) and one for lights (both upstairs and down).

Spur from the lighting circuit 5a breaker in 1.5mm for about a foot then connected with terminal block to 6mm cable feeding a single socket. This obviously needs to be changed.

Spur from ring final 30a breaker in 2.5mm cable feeding three sockets and a further light under the stairs, not connected via a fused spur.

Spur from 40a breaker in 2.5mm cable feeding 6 sockets in the conservatory.

Truly bizarre.

Question is, how many spurs can you have off a single MCB? I'm thinking it wuold be much better to change the cable feeding the single socket to 2.5mm and moving to the 30a MCB and then taking the current spur connected to the 30a MCB from this single socket. There would be a 13a fused connection between breaker and the first socket on the run.

For the conservatory spur (well, radia really!) I was thinking of also adding this to the ring final MCB, again with a FCU between MCB and the first socket.

How does this sound as a temporary until the CU can be changed? Are you allowed two spurs from one MCB? It's the safest option I can think of for now.

The entire installation is protected by a 30ma RCD between meter and CU.

Cheers folks

Don.

well aside from the regs contravention of having the whole thing on one 30mA......

you can have as many spurs as you have sockets. Where you connect them from exisitng sockets, j/b's or the MCB is ireelelvant. A fused spur can feed as many sockets as wish, but would still be treated as one spur for totting up

whole thing sounds a right mess anyway:rolleyes:
 

Reply to Spurring from MCB in the Canada area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
652
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
610
Can someone explain electrically why we can spur unfused from a ring final on a 32a breaker when the cable is 2.5mm rated at max 27a?
Replies
4
Views
925
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
915
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock