Is it okay to spur off a ring in 4mm to serve 4 x sockets, without a fcu before the first socket??
Yeah that’s what I thought but I was being told otherwise. I thought a spur would still be required even though 4mm can carry 32aNo, an unfused spur is only permitted to feed one point regardless of cable size.
It’s a shed at the other side of the gardenFour sockets I would be trying to extend the ring.
Is it okay to spur off a ring in 4mm to serve 4 x sockets, without a fcu before the first socket??
It’s only a desk for a computerWhat’s going into a shed that’s going to draw more than 13A?
If it’s anything bigger, I’d try to get it on its own circuit direct from the consumer unit.
It’s a shed at the other side of the garden