Is it okay to spur off a ring in 4mm to serve 4 x sockets, without a fcu before the first socket??
 
No, an unfused spur is only permitted to feed one point regardless of cable size.
 
No, an unfused spur is only permitted to feed one point regardless of cable size.
Yeah that’s what I thought but I was being told otherwise. I thought a spur would still be required even though 4mm can carry 32a
 
Why use 4mm? If you have a larger load than 13 amp FCU extend the ring in 2.5
 
Four sockets I would be trying to extend the ring.
 
What’s going into a shed that’s going to draw more than 13A?

If it’s anything bigger, I’d try to get it on its own circuit direct from the consumer unit.
 
Is it okay to spur off a ring in 4mm to serve 4 x sockets, without a fcu before the first socket??


You could have 16amp mcb assuming you have rcd on the ring final.
 
What’s going into a shed that’s going to draw more than 13A?

If it’s anything bigger, I’d try to get it on its own circuit direct from the consumer unit.
It’s only a desk for a computer
 
It’s a shed at the other side of the garden

It would be common sense to install a SFCU to allow it to be easily isolated whenever a fault in the external wiring occurs so that the rest of the circuit can be re-energised easily.
 
If you can run a dedicated radial circuit from the CU
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Glasgow
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Spurring of ring final circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
Welsh_sparky_21,
Last reply from
7029 dave,
Replies
10
Views
344

Advert