spurs

  1. Pretty Mouth

    Ring finals and fused spurs

    Evening all. The OSG says "As a rule of thumb for rings, unfused spur lengths should not exceed 1/8 the cable length from the spur to the furthest point of the ring.". Okay, so what is the maximum length for a fused spur then? I don't seem to be able to find the answer in the OSG or BBB...
  2. R

    Power wiring for fan Spurs

    Hi Just wondering if anyone would be able to help with this, have a circuit in a room with two fans one inside and one outside to be controlled by a double pole switch, and to be connected into spurs above the ceiling, anyone be able to tell me how to wire correctly?
  3. Thomas Connolly

    Spurs.... Not the football type!

    Hi Guys Need the experts advice again please . Recently added a new double socket in a kitchen off of the existing ring final. At last minutes notice I was asked to see if I can add an outside light by the back door. (Which is right next to the new socket that's just ben added) The question...
  4. D

    2 questions - Existing ring main mapping, and rules on spurs

    Hi Just getting started with a view to DIY electrics on my house extension in a few months time, and ideally would like to map out the current circuits so I can plan the best way to join up, or where new circuits may be required etc. 2 Questions I reckon I can do some DIY non-live testing of...
  5. M

    2 spurs from a Junction Box....worried?

    Hi folks. I cut one of the cables on my ring circuit, attached the 2 now separate ends to a new 30a junction box, and then run 2 additional spurs from the same junction box, using 32a twin and earth, on the end of each of these new spurs is a twin plug socket with usb. I did the work with my...
  6. Daniel Shepherd

    Domestic Two fused spurs from one current socket?

    Hi, I'm doing some work on a room I want to convert into an office space. It currently has three sockets in it. One has two neutral and two live wires connected to the socket, the other two have 3 live an neutral wires (this wiring is done circa mid 60's we think. I plan to add about 2000kw...
  7. M

    New spurs stadium having major problems

    Ok without any football team references... Mace are the managing contactor and spurs have nominated contactors. So mace wont be liable to any delay clauses due to this. I read in construction manager journal approx 500 sparks ( including supervision ) but not sure. Anyway my point is with that...
  8. Steve_bcs

    Advice sought on spurs off spurs

    I am refurbishing a house i bought last year & looking for thoughts on whether the following existing wiring is right/ safe. I dont think it is but would like to check as it looks like spurs of a spur to me. The CU was just replaced by local electrical contractor & all circuits are he says...
  9. A

    Ring main consisting of only spurs

    Hi, this is my first time on this forum so I hope I'm in the correct section. I've come across a strange socket wiring set up in my own home. I was baffled at first as to how at the consumer unit I had a ring main set up (2x 2.5 T&E fused at 32A) but radial setup at each socket (1 cable). What...
  10. Z

    Adding a spur to a spur

    I have a socket which is connected off the main circuit ring. Just wanted to know if it's possible to add another socket spurring off this second socket? (Please see attached image.) If it's against regulations, then 1) what's the worst that could happen? (Will my circuits blow up?) 2)...
  11. S

    Domestic Shower pump power work/alterations

    Afternoon to all! I have to replace my current shower pump as it's on the way out, it's loud at the best of times so I have taken the opportunity to replace with a quieter unit but my problem is it's a different make and as a result the power supply is also different, the new pump comes with a...
  12. nyb

    Multiple spurs off double socket

    Hi I recently purchased a house (built and wired in the 80s). I removed one of the sockets to do some wallpapering and I noticed that it has 4 hot+neutral (+earth) wires connected to the double socket (and I'm assuming it's all solid core 2.5mm wiring??). I'm not sure if it's connected in a...
  13. C

    Adding single radial sockets to Ring as spurs

    Hi, I have recently completed an intensive electricians course and I am at the stage where I am trying to get practical experience wherever I can. One of my jobs, which I am planning to use to join a competent person scheme, is to change my consumer unit and wire up my extension. At present...
  14. S

    spurs

    what is maximum amount of spur sockets taken from a main , the main amperage can be changed easily the wiring is 2.5 and a ring main is not possible without a lot of work as this is a large old house which has been wired this way , there will only be one large consumer a water heater .
  15. G

    Problem neutrals

    Problem with neutral. The other day we had a problem with a circuit not working correctly. The circuit is a radial,wired in 4mm singles,in metal trunking powering 4 switched fused Spurs. The circuit had previously been dead tested,with no apparent problems. However when the circuit was...
  16. D

    Grid switch for kitchen appliances

    Ok, I'm wondering if someone could clarify this one for me.. I am in the middle of a rewire, and a kitchen company has designed the kitchen layout (including electrical layout).. They have requested that I fit all of the fused Spurs for the appliances in a utility room adjacent to the kitchen...
  17. L

    Fused Spurs under sink?

    Hi I have a situation where there are Spurs under sink zone 2. would it be ok if fittings where ip rated or fittings were enclosed in ip rated housing. the circuit is protected by an rcd . Lim pretty new to testing by would appreciate any advice. Ive tried to find solution but was not able to...
  18. S

    Spurs off Spurs on radial circuit

    So you can spur off Spurs on a radial socket circuit, is this because the cable is protected via a 20amp breaker at the board compared to 32amp on a ring?
  19. B

    How to tell if socket is on ring or spur off spur

    Ok so you have the classic to cables in back of socket. Spurs should be identifiable through higher resistance but if very short spurs and it's an older install and you want to break into the ring to add another socket. You could be creating a spur off spur off spur? How do u go about being...
  20. D

    RCD required?

    Hi guys, Just a quick query here. I have just gone into a property and done a EICR. Its a rewireable fuseboard with no rcd protection on any circuits. The main house ring circuit has an occurence with a spur off a spur. Easy to rectify i know but as i am going to to re-feeding the sockets, is...
  21. H

    EICR Code Help!

    Hi just after a quick bit of guidance, I have completed an EICR, and found a spur of a spur on a ring final circuit, there were no signs of thermal damage and the sockets are in 2 bedrooms and feed table lamps and phone chargers. I know this is a no no in terms of the regs, but what would...
  22. happyhippydad

    2 spurs coming from the same socket - NOT a spur from a spur!

    Hello all.. I have recently added a spur for a customer and it got me thinking again about how many spurs could I actually take from the same socket! The only socket I could use to take the spur from was on the ring and was already feeding a spur. Now I could have extended the ring but after a...
  23. D

    Ring Circuit Question

    Hi all, In my house I have a ring main which covers two floors, from which I have created two spurs with 2.5mm cable. I am drawing 3000W on each spur and on the ring sockets probably around 500w making a total of 6500w. Do you think this is dangerous as it is exceeding the 24A rating on 2.5mm...
  24. J

    Grid switches

    hello. jut a quick q on grid switches and what your ways to install them are.. eg. using 20A DP switches with a fuse next to it or just install a FCU to hard wire applience in, there for not fusing at the grid. would you run it in 4mm, 2.5mm or 6mm radial or would you run it of the ring...
  25. M

    Continuity of ring final circuit..... can somebody help please !!!!

    Im currently studying electrical and im up to dead tests. ive reached continuity of ring final circuit on my scenario cd , in therory i understand the procedure and what to do but im a little un sure on finding the mid point on the sockets . please can sombody go threw it step by step in...
  26. L

    Domestic fused spurs

    i am considering starting an av install in the front room. on the wall i am considering i have a socket, which i would like to run a quantity of fused spurs off. these would be for the component parts if the install. i do not want a selection of double sockets each with a plug in, as i feel this...
  27. S

    Domestic Does my Irish Qualification allow me to work in Scotland???

    Hi All, I was working for an Access Control company for about 18 months and was told that my Irish Electrical Qualification was sufficient for me to do basic things like wiring spurs etc. I have recently started my own business doing CCTV,Alarms etc. I have found conflicting info about whether...
  28. N

    wiring in dado trunking

    hi guys quick question, got sent out to a job today to connect in sockets that are lying on the floor in dado trunking for office computers etc, the whole room is wire in a ring protected by a 32a mcb to 5 seperate 20amp double pole switches, these switches feed about 5 or 6 sockets each on a...
  29. happyhippydad

    Why are you only allowed one spur per socket on a RFC?

    This is something I have been racking my brain over for ages and its doing my head in!! :crazy: Please could someone explain why you are only allowed to have one unfused spur per socket on a RFC? I'll explain a little why I'm confused. A ring main is allowed as many sockets as you like on the...
  30. S

    Todays job

    Went to install a few extra sockets into dado trunking in an office, nice easy one for a saturday morning. Checked ring continuity at first socket to tap into ring, no continuity, went on to discover spurs off spurs big style, 6 sockets spurred off ring on one side of office, 7 spurred off ring...
  31. G

    Domestic my house rewire kitchen circuits help

    Hi guys started a thread recently about my house rewire which im starting soon but i still have some issues, as ive said in the past i very rarely do domestic work so thats the reason im asking but here goes... im just after a bit of info and reassurance on kitchen circuits im getting an...
  32. G

    MK Logic fused spurs

    Does anybody else have problems with the design of the fuse holder of an MK Logic fused spur? I hate the bloody things! They can be very difficult to remove sometimes and can easily be chipped when levering away with a screwdriver. Also, latching back in can be a real test too. I've used MK...
  33. C

    Fused spur

    Hi, I'm installing an outdoor light and am going to spur off a socket ring circuit, I was going to spur off a socket that was closest to where the installation is going up, but have realised that there is a spur coming off the socket outlet. Is it possible the have two spurs coming off the same...
  34. J

    Double pole. Kitchen installation with appliances.

    Hi there. Just looking for a bit of advice, I recently carried out an electrical installation within a kitchen, I never installed any new cables just repositioned the existing cabling. I used two switched spurs to switch a under shelf fridge and freezer fed from an existing ring circuit...
  35. F

    Domestic CU change and spurs off a ring main final

    If i change a domestic CU and find that some of the socket outlets on a ring main final cct are unfused spurs or maybe unfused spurs from unfused spurs, and if the Zs complies at each s/o & IR test OK - can i leave as is ? or do i need to alter the spurs in the cct to comply with 17th edition.
  36. G

    178m sq floor area for socket outlets

    Hi all this is first time I've posted so appologies if I've missed anything out. Recently just done a i&t and the ring main in one part of the commercial building is completely "ballsed up" to say the least. Spurs off spurs with rings of them and even more spurs off them. Going to have to...
  37. D

    Fused Spurs?

    Looking for some advice on what the requirements / qualifications are to install fused spurs. I install security systems for a living and always use a sparky to have spur ready before we go in and install. I want to be able to install spurs myself, where should I start in terms of...
  38. A

    simple question on switch spurs

    Does a switch spur for am integrated kitchen appliance, like a fridge or washing machine, need to be within 2 meters of it or is that just for ovens and hobs? Also, do they need to be on switched spur? O and one more lol. Need to ask or I wont learn :p is it best to have the washing machine on...
  39. T

    Testing.. Never goes right..

    Practicing again... TN-CS Supply New Built Home Tested ring final circuit.. P - 0.34 N - 0.34 CPC - 0.59 ________________________________________________ N1 - P2 = 0.70 N1 - P2 P1 - N2 = 0.16 P - N Sockets.. 1- 0.19 2- 0.16 3- 0.17 4- 0.17 5- 0.18 6- 0.16 7- 0.21 8- 9- 0.18...
  40. P

    help to price this job

    hi just need some advice on prices for this job .the job this to supply 2x 16 amp blue & switch spurs ,single phase and wire back via trunking for a bout 7 mtrs long back to the d/b supply cable, spurs,plastic conduit ,2x blue plug outlets,20 AMP TYPE B mcbs and installtion certifcate, the job...