Hi everyone.
I basically wanted to check to see if what I propose is correct.
I had an electrician come round (pre covid) to install power to my garage (Detached from house). This is the setup he used.
What I want to do is connect the light fitting up (but not stick a plug on it as some people has told me to do).
My plan is to spur off the garage socket to a 5A switched FCU, which will also act as a light switch then connect the existing light to this switch. Does that seem ok?
Also, as the garage is protected by the 13A FCU (inside the house and before the first garage socket) can I have multiple sockets (and the 5A FCU) off this spur?
Thanks in advance.
M
I basically wanted to check to see if what I propose is correct.
I had an electrician come round (pre covid) to install power to my garage (Detached from house). This is the setup he used.
- Spur off socket on ring main a short distance to a 13A switched FCU
- Cable from the FCU through external wall to outside junction box.
- From junction box through armoured cable into garage.
- Armoured cable into 1x 2G socket.
What I want to do is connect the light fitting up (but not stick a plug on it as some people has told me to do).
My plan is to spur off the garage socket to a 5A switched FCU, which will also act as a light switch then connect the existing light to this switch. Does that seem ok?
Also, as the garage is protected by the 13A FCU (inside the house and before the first garage socket) can I have multiple sockets (and the 5A FCU) off this spur?
Thanks in advance.
M
- TL;DR
- I have spurred off house socket to 13A FCU, which goes to garage. My plan is to spur off the socket in the garage to a 5A switched FCU, which will also act as a light switch then connect the existing light to this switch. Does that seem ok?