Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the socket and take it down to 20a or 16a instead via a submain to allow for that extra kW if needed. If the cable size was sufficient for the length. For a garage sub main wired in swa. (32a ring circuit). In theory if you had sockets on a 16a rcbo and lights on a 6a then it's under the 27A limit generally a 2.5 can take. Thanks
 
Might help if you actually stated what you are trying to achieve as apposed to random disjointed bullet points.
 
Apologies. My mission is to achieve a bigger supply to a garage of 16 to 20amps, rather than 13a. I'm not trying to achieve anything physically, I just want to know if it's possible, forgetting about what the spec is for the job. Is it allowed?
 
Apologies. My mission is to achieve a bigger supply to a garage of 16 to 20amps, rather than 13a. I'm not trying to achieve anything physically, I just want to know if it's possible, forgetting about what the spec is for the job. Is it allowed?
Yes you could
 
Yes you could
Care to explain your reasoning?

You're stating that a 'submain' which is 'spurred' off a ring final circuit, protected by a device that'll happily permit in excess of 27A for hours on end is permitted.

The IET are clear about what is permitted to be spurred of this type of circuit and they don't include 'submain protected by 16A or 20A device'.

Maybe the OP will proceed on the basis of 'some person on the internet said it was okay', but I'd advise against doing so and point out that their proposal isn't permitted on a regulatory basis and is also flawed on a theoretical level.
 
Care to explain your reasoning?

You're stating that a 'submain' which is 'spurred' off a ring final circuit, protected by a device that'll happily permit in excess of 27A for hours on end is permitted.

The IET are clear about what is permitted to be spurred of this type of circuit and they don't include 'submain protected by 16A or 20A device'.

Maybe the OP will proceed on the basis of 'some person on the internet said it was okay', but I'd advise against doing so and point out that their proposal isn't permitted on a regulatory basis and is also flawed on a theoretical level.
You are only allowed to supply equipment to BS1363 via a spur from a ring final circuit (433.1.204). As that standard (to the best of my knowledge, anyway) does not contain devices rated to greater than 13A then it's mechanically impossible to exceed the 13A barrier.
 
You are only allowed to supply equipment to BS1363 via a spur from a ring final circuit (433.1.204). As that standard (to the best of my knowledge, anyway) does not contain devices rated to greater than 13A then it's mechanically impossible to exceed the 13A barrier.
OP is asking if instead of using a 13A fcu they could spur using a 16A or 20A device as a 'submain' to supply a garage.

"instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the socket and take it down to 20a or 16a instead via a submain to allow for that extra kW if needed"

"My mission is to achieve a bigger supply to a garage of 16 to 20amps, rather than 13A"

Their proposal omits 13A protection mandated by the wiring regulations in such instances.

The omission of 13A protection is clear in their first sentence, with everything else clarified in their follow up post.

This proposal would not be permitted and for good reason.
 
Last edited:
OP is asking if instead of using a 13A fcu they could spur using a 16A or 20A device as a 'submain' to supply a garage.

"instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the socket and take it down to 20a or 16a instead via a submain to allow for that extra kW if needed"

"My mission is to achieve a bigger supply to a garage of 16 to 20amps, rather than 13A"

Their proposal omits 13A protection mandated by the wiring regulations in such instances.

The omission of 13A protection is clear in their first sentence, with everything else clarified in their follow up post.

This proposal would not be permitted and for good reason.
We're on the same page here matey, my (possibly poorly worded) post was basically saying that you can only hang BS1363 (eg a 13A fused spur) rated equipment off a RFC. To use a 16A or 20A device to protect the 'sub main' would be by it's very nature a different BS standard - either 3036, 60898, 61009..... etc and therefore not comply.

And that's before we get to discussion about whether it's a good idea or not!! (Hint: It's not).
 
We're on the same page here matey, my (possibly poorly worded) post was basically saying that you can only hang BS1363 (eg a 13A fused spur) rated equipment off a RFC. To use a 16A or 20A device to protect the 'sub main' would be by it's very nature a different BS standard - either 3036, 60898, 61009..... etc and therefore not comply.

And that's before we get to discussion about whether it's a good idea or not!! (Hint: It's not).

Problem with threads like this is OP has been told it's fine and hasn't been back since.

They're quite possibly in screwfix buying a small din rail enclosure and 20A MCB.
 
I agree with @Rockingit 's post regarding rings and BS1363 accessories, from a compliance point of view.

However... the arrangement where a garage is spurred from a ring final, via an 13A FCU, is not ideal in practice. I have had to deal with a few burnt out FCUs where it has been installed this way. Real world, they don't seem to be reliably up to the job.

IMO, while technically not compliant, it would actually be an improvement to protect the spur to the garage with a 16A breaker instead of an FCU. They are more reliable, and the time/current curve is very similar to a 13A BS1362 fuse anyway.

The lighting could likely be protected by the same device, without further fusing down, or the 6A breaker could be wired downstream of the 16A one.
 
I agree with @Rockingit 's post regarding rings and BS1363 accessories, from a compliance point of view.

However... the arrangement where a garage is spurred from a ring final, via an 13A FCU, is not ideal in practice. I have had to deal with a few burnt out FCUs where it has been installed this way. Real world, they don't seem to be reliably up to the job.

IMO, while technically not compliant, it would actually be an improvement to protect the spur to the garage with a 16A breaker instead of an FCU. They are more reliable, and the time/current curve is very similar to a 13A BS1362 fuse anyway.

The lighting could likely be protected by the same device, without further fusing down, or the 6A breaker could be wired downstream of the 16A one.
Whether we have a different approach from an engineering perspective or not, I think we can all agree that this forum should only, ever, give advice which is compliant.
 
Whether we have a different approach from an engineering perspective or not, I think we can all agree that this forum should only, ever, give advice which is compliant.
The IET doesn't seem to agree with that sentiment, and suggest connecting equipment via a 16A breaker in the OSG. This is from appendix H, P211:

Permanently connected equipment should be locally protected by a fuse complying with BS 1362 of rating not exceeding 13 A or by a circuit-breaker of rating not exceeding 16 A and should be controlled by a switch, where needed (see Appendix J).
 
Care to explain your reasoning?

You're stating that a 'submain' which is 'spurred' off a ring final circuit, protected by a device that'll happily permit in excess of 27A for hours on end is permitted.
Any single point of the ring final could do the same at a double socket outlet.
The IET are clear about what is permitted to be spurred of this type of circuit and they don't include 'submain protected by 16A or 20A device'.
To be accurate, while the regs no longer offer it as a 'deemed to comply' solution, that's still a long way from being a non-standard (as in doesn't comply with BS 7671) installation. I think the worst you can say is non-conventional. Much of the "rules" for ring circuits have been taken out from the normative parts BS 7671 over the years and now only exist as general guidance. It's likely a 16A MCB fed from as ring could still comply with all of BS 7671's requirements
Maybe the OP will proceed on the basis of 'some person on the internet said it was okay', but I'd advise against doing so and point out that their proposal isn't permitted on a regulatory basis and is also flawed on a theoretical level.

My reply to the OP was in relation to :

Johnconnor said: Apologies. My mission is to achieve a bigger supply to a garage of 16 to 20amps, rather than 13a. I'm not trying to achieve anything physically, I just want to know if it's possible, forgetting about what the spec is for the job. Is it allowed?

The OP asked if it was possible, and also stated that he wasn't going to do anything physical.
 
Last edited:
The IET doesn't seem to agree with that sentiment, and suggest connecting equipment via a 16A breaker in the OSG. This is from appendix H, P211:

Permanently connected equipment should be locally protected by a fuse complying with BS 1362 of rating not exceeding 13 A or by a circuit-breaker of rating not exceeding 16 A and should be controlled by a switch, where needed (see Appendix J).
I pretty sure this was at one point in the Regs I'm not going to hunt for it but it rings a bell.
 
Nothing, and I didn't say anything was.

What I said was that you cannot take a distribution circuit (aka submain) from a final circuit.
If you extend a final circuit into another building then it is still a final circuit.
What would be wrong with a say a 6mm radial ?
 
Any single point of the ring final could do the same at a double socket outlet.

To be accurate, while the regs no longer offer it as a 'deemed to comply' solution, that's still a long way from being a non-standard (as in doesn't comply with BS 7671) installation. I think the worst you can say is non-conventional. Much of the "rules" for ring circuits have been taken out from the normative parts BS 7671 over the years and now only exist as general guidance. It's likely a 16A MCB fed from as ring could still comply with all of BS 7671's requirements


My reply to the OP was in relation to :

Johnconnor said: Apologies. My mission is to achieve a bigger supply to a garage of 16 to 20amps, rather than 13a. I'm not trying to achieve anything physically, I just want to know if it's possible, forgetting about what the spec is for the job. Is it allowed?

The OP asked if it was possible, and also stated that he wasn't going to do anything physical.
The OP asked if he was "allowed" to take use 16A or 20A protection from an unspecified device to give himself an extra 3kW on a garage supply. The OP stated that their intention was to do so by "spurring" this unspecified protective device off a ring final circuit in place of a fcu. Her went on to clarify that this would supply 16A & 6A RCBOs in the garage.

You responded by stating that "he could".

These are the facts and let's not dress it up by claiming any information beyond that posted.

The advice wasn't in line with regulatory requirements and has the potential for loads considerably above that permitted to be carried by the cable intended for use if 20A protection is used at the proposed 'spur'.

Edit: I'm not the forum police and you're free to post as you please. On this occasion I believe the advice to be inappropriate and challenged it.
 

Reply to Spur off 32a house socket form garage for 20a supply. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
Hi I've got a job that i've been asked to quote for and i'm struggling with how to do it the best way. It's a summerhouse and the customer only...
Replies
17
Views
3K
This is a question with probably so many answers and solutions, but I wondered how people would do it. I have a clients house which already has...
Replies
7
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello, I'm no Electrician, but I think I have a understanding of the basics. Few years ago We had our Garage supplied with power by and...
Replies
8
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock