This is a question with probably so many answers and solutions, but I wondered how people would do it.

I have a clients house which already has one submain on a 40A MCB to a Garage with a 20A RCBO radial and a 6A RCBO lighting circuit + a spare 32A RCBO. Selectivity not an issue.

They need a 2nd sub main in a new summerhouse which will be a gym (Well I say a gym, it'll have one treadmill), plus an outdoor inflatable hot tub (the type that can be plugged in, although it can draw 2.5kW).

It would be tricky (but not impossible) to run a second cable from the main board to the summerhouse, but the main board is in the middle of the house with no easy route to the outside, and I'm unable to follow the route of the first cable. (House has an isolator, so I could split off the mains too). This would be the best option granted, but the hardest to actually do given the location of the board.

I could use the spare 32A RCBO and run a cable from that to the new sub main, that route is far easier, but obviously I would need to take care with the loading. Luckily the garage has a negligible load.

Third option which I expect will be frowned at is to 'T' off the cable that goes to the garage, and route a cable from that to the summerhouse, thus the garage and the summerhouse come off the same 40A MCB in the main house, rather than via the 2nd consumer unit in the garage.

How would you do it ?
 
Last edited:
They need a 2nd sub main in a new summerhouse which will be a gym (Well I say a gym, it'll have one treadmill), plus an outdoor inflatable hot tub (the type that can be plugged in, although it can draw 2.5kW).

So the only thing that will be in the summer house (ignoring lights) will be a treadmill & a plug in hot tub? No heater in there for winter or anything else?
 
It looks like a 4mm Hi-Tuff cable (certainly isn't SWA), I measured it's approximate length from the board as about 10m, clipped direct mostly, just underground for about a metre or so under a path between the house and garage.

I was going to say just extend the existing submain to feed another CU in the summer house.
But if its 4mm on a 40A MCB and Hi-Tuff underground then I'd be avoiding using that circuit and advising the customer about these issues.

Why does it need a submain in the first place? Could you not just run a socket circuit to the summerhouse?
 

Reply to Multiple sub mains, how would you do it ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
766
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock