Thomas Connolly

Hi Guys
Need the experts advice again please .

Recently added a new double socket in a kitchen off of the existing ring final.

At last minutes notice I was asked to see if I can add an outside light by the back door. (Which is right next to the new socket that's just ben added)

The question being, if I were to add a 3A FCU from the spur I've just added to then feed the outside light, this would be classed as spurring a spur right?
So would a better option be to add a 13A FCU before the new spur and then have the outside light feed off of the double socket?
Realistically I can't take the feed for the light from anywhere else but don't want to disappoint and turn down the request.

As always, your help is very much appreciated .
 
Thanks Guys .
Very informative as always. I've read the Regs and as above have seen that u u need the FCU to be prior to the new socket if I'm to add the outside light as well.

My second question is, purely out of curiosity is, can I wire both the new socket AND the outside light coming from the FCU or will the load blow the fuse (13A) or only the double socket from the FCU and then have the outside light coming from the socket?

Thanks .
 
It doesn't matter where you connect the external light from providing the spur protects both. What is currently connected from the socket and I assume rcd protection is provided.
 
Ok. It would be easier for to run the light straight from the FCU. I just wasn't sure if I could have the wiring for the light and the socket in the FCU.
That's ok to do is it?

RCD wise. It's a very old build so no RCD on the ring at the CU. Would making the FCU an RCD protected FCU be sufficient?
 
Are you electrically qualified because the socket you added would have required additional rcd protection.
 
Via the FCU or at the Board?
Long story short, qualified as a domestic installer last year, was working as an apprentice with an electrician, he left unduly so I've been asked to do two small jobs in his absence.
This being one of them.

So because I've added a spur to an existing ring, I need to upgrade the whole board so it's RCD protected?
 
So at present are you working with no guidance because it is a bit worrying you have installed a socket without additional rcd protection. Assuming this is a domestic site the new light fitting also requires additional rcd protection.
 
At present yes until the new spark arrives. I was under the impression that an additional socket was something the home owner could do?
So an FCU prior to the new socket wouldn't be enough?
I'd have to upgrade the entire board?
 
At present yes until the new spark arrives. I was under the impression that an additional socket was something the home owner could do?
So an FCU prior to the new socket wouldn't be enough?
I'd have to upgrade the entire board?
Not necessarily.
 
@DPG I can test and inspect but the likelihood is we will get someone in to do so.

@Pete999 I thought an addition to an existing installation wouldn't require a new board. Would it be necessary to do so in this instance!?
 
Thanks for confirming.
The work you do will need to be RCD protected but not necessarily the whole consumer unit. Obviously depending on the circumstances then different methods of achieving this may be considered, including RCD protection of the whole circuit.
 