Usually,someone decides to manually operate one of the contactors,whilst the other is energised,to "see if it changes the outcome" .....eye protection,obligatory :(

Any SD starter built or modified since 2004 needs a mechanical interlock along with an electrical interlock to the contactors to stop that from happening.
 
Any SD starter built or modified since 2004 needs a mechanical interlock along with an electrical interlock to the contactors to stop that from happening.

Hi Rob, which regulations are you referring to that states mechanical interlocking is mandatory?
 
I'll dig it out when I get back to my office on monday.

It's not specifically stated in 60204-1 but a standard that it quotes. I'll dig out an post the section.
Thanks Rob I would be interested as well, whilst not doubting you in any way, just for my own curiosity.
 