Hi folks,

When I connect up a motor in Star supply goes to U1 / V1 / W1 and links fitted across U2 / V2 / W2 (depending on how terminals are marked)

Out of curiosity what would happen if supply was connected to U2 / V2 / W2 and U1 / V1 / W1 were linked out?

My initial thinking is motor would run in reverse, however as assumption is the mother of al xxxxups though I'd ask.

For the record I've not seen or done this so can't specify motor type, sort start, VSD or anything. It's purely a "what if" type thing.
Its amazing how the mind can wonder when you have too much time on your hands!

Cheers in advance.
 
  • Like
Reactions: 1 person
http://www.electriciansforums.co.uk/commercial-industrial-electrical/10495-star-terminal-block-arrangement.html
 
  • Like
Reactions: 1 person
Never really give it a thought but now you ask i would say nothing would change it will still work as before.

Dont forget its the supply phase rotation that decides the direction of the motor which hasn't changed you have only flipped the windings around.

Exchanging 2 phases is the way to normally change the direction either by inverter parameter option or physically changing them over... this changer the direction the magnetic field rotates in.


Hmmm! got me thinking now!..

Note! ... This is the case for the 3ph standard induction motor under discussion and some motors will have direction altered when windings are reversed.
 
Last edited by a moderator:
I know what you mean about getting you thinking, I was reading a different thread and for some reason just started thinking about this.

As I say it's of no importance at all, just more of an "If a tree falls in woods" type thing.

Cheers.
 
Its this kind of thinking and curiosity that will put you one step ahead of the next guy because you seek understanding instead of parrot fashion learning and when a difficult issue arises you'll be the one that is more likely to resolve it so dont eat yourself up at questioning such a thing.
 
I don't think it would make a difference i am pretty sure the star point is whatever you make it when you wind the motor, and as DW said to change phase rotation, you simply swap any 2 of the 3 phases.
 
(Trainee).

Assuming 3ph standard induction motor...

Your motor will still rotate in the same direction. The only thing that will change is the rotation phase relative to your supply. By which I mean, say you had a marker on your shaft, a high speed camera and an oscilloscope so that you could see the voltages of all three phases. With your supply going to U1, V1, W1 (U2, V2, W2 shorted out) your marker would be in a certain position (say, 2 o'clock) when L1 was at the peak voltage. With your supply going to U2, V2, W2 (U1, V1, W1 shorted) your marker would be at the opposite position (in this example, 8 o'clock) when L1 was at the peak voltage.

If your motor's shaft position depended on the absolute phase of the incoming supply, or (perhaps more likely) interacted with another motor such that the absolute phase mattered (imagine two motors whose shafts were connected by something like a chain... now try twisting one of them by [360 deg divided by the number of poles] ) then it would matter. If it's a standalone system... meh.

Similar thing if you rotate all your connections, e.g. instead of:

L1 -> U1
L2 -> V1
L3 -> W1

... you did:

L1 -> W1
L2 -> U1
L3 -> V1

... the direction would be the same, but the marker on your shaft would be 120 deg different (ahead?).

(Trainee).
 
Last edited:
40 years of playing with motors and never given it a thought. Drew it out and then something stirred in the back of my mind. I have done it when I had to change the supply cable to a motor. It was a big cable so it was easiest to swap the star point over.

Now here’s another one for you consider. What happens if the star point is swapped on a ∆Y Dyn11 transformer?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Star Motor Connection
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
Schneker,
Last reply from
Bobster,
Replies
9
Views
5,932

Advert