To cut a long story short. Conduit is fine for the earth. Providing good test results.

Previous sparkys would have the pound signs in their eyes. The tennant would believe them that there is no earth and that this is a big thing.

Maybe if there was more tradesmen like you out there, people wouldn't be getting ripped off by cowboys rewiring perfectly good cables and systems.
 
When you say figures complied with regs.... did you X0.8 the regs value. E

Eg.. Type B6 BS60898 Max Zs in Regs 7.67. Actual Allowed is 6.13.

Just Checking...:policeman:


it was well within max allowed usuing 0.8 rule of thumb
 
When you say figures complied with regs.... did you X0.8 the regs value. E

Eg.. Type B6 BS60898 Max Zs in Regs 7.67. Actual Allowed is 6.13.

Just Checking...:policeman:[/QUOTE

Not quite
Max zs in regs 7.67 max allowed = 7.67. Its only when say circuits put in service or not been carrying there Ib ( design current) that you use the 0.8 factor.
Circuits that have been in service fully loaded carrying there Ib for a period ( say an hour) Max as is that stated in table 41.3 ( for 60898 mcbs)
see appendix 14 in bgb
 