Unfortunately, in reality, it's almost always possible for an end user to demand more than their supply is capable of handling, which is why OCPDs are installed. Take a look around your home and ask yourself what would happen if I plugged a 3kW kettle into every socket in my kitchen.
The OCPDs in the board are there to protect the installation wiring and little else and the suppliers OCPD is there to ensure the install as a whole doesn't exceed it's capabilities.
But it's still not clear what's tripping, and when the tripping started. You're just basically pointing the finger at the spark who you've been told designed and installed this 4 years ago, so I'll say this... if these tripping problems were not present when the installation was signed off 4 years ago (if they were, they should have been reported to the original contractor), and only started in say the last 18 months or so I'd suggest the client has changed something and introduced equipment that pushes the demand beyond the capabilities of the installation (as designed 4 years ago based on the information available to the spark at the time).
I actively try and encourage my clients to include some additional capacity 'for the future' but there comes a point where it's not practicable or financially viable. If it was a new business, they possibly had budget constraints so the spark may have been financially impeded. There's so many factors that could have played a part in his decision making process and you can pretty much guarantee you won't get the negative points from the client since they obviously want you on their side.