I work in water display automation and often call in sparks to test kit ahead of going on display. It's amazing how many look for additional ways to test submersible pumps. It's as if you guys can't accept a simple days work
It's double insulated, the end. Test IR. That's all you need to do and all I expect. If it holds up, pass - if not, bin.
On some seriously top end (££££) multistage submersibles you might get involved in deeper testing to see if it's worth breaking into the pump and refurbishing it. But in general, the insulation showing signs of failure alone will result in the pump being condemned and a new one put into service.
I understand you might want to be really 'on it' when dealing with electrical kit that lives in water. But rest assured, water is at best a shockingly bad conductor in real terms. Most of the failures we identify in house are not initially discovered at the time of electrical testing, but when we enter a pool and feel an odd tingling sensation, especially noticeable if you have any broken skin. Might sound a little flippant, but consider that millions of children have their arms in fish tanks with submersible filter pumps that are never tested. Of course, many do fail and many moons ago I worked in the ornamental aquatics trade - a tingle up the arm as people serviced their fish tanks was often the deciding factor in spending £30 on a new pump/heater, whatever had failed.
If you want to feel warm inside that you have done all you can, don't just test. Open up the plug/panel and physically check and re-torque the earth at each terminal back to the main circuit. That way, no matter what fails on the pump, the current has a place to go that is easier than water>victim.