Deleted member 9648

Evening all,
I have been asked to refurb a steel trailer used by a sheep shearer. The unit presently has 2 twin IP sockets which need replacing,and is fed by a 13a plug which the shearer either plugs into a small duel voltage genny,or straight into whatever mains supply is available on site.There are arrangements to protect the plug when stored/towed.
There is currently no RCD on the trailer,and I was thinking this was essential given the uncertain supply arrangements. Question is would a standard RCD provide additional protection when the supply is from the genny?...I don't have a great deal of experience with generators so am not sure. Also would you bond the trailer frame...no earth electrode would be in use when supplied by the genny?
 
Interesting one.

I believe the small generators generally produce a more square wave output (even when they say pure sine wave!) however from the point of view of the RCD this would be similar to a standard sine wave. The pattern would be regular alternations through zero.
I cannot see a Type B or A RCD being any more sensitive to this pattern, but both would also work.
I think type A has to have a DC current that crosses zero and a type B just a dc current, including the type A pattern.

Bonding wise the trailer is presumably being used outside so the earth will be a constant potential against different from the supplied earth and so bonding would be pointless.
I would probably earth the trailer instead, with flexible leads being slung about the flex could easily become worn and short to the trailer.
 
Interesting one.

I believe the small generators generally produce a more square wave output (even when they say pure sine wave!) however from the point of view of the RCD this would be similar to a standard sine wave. The pattern would be regular alternations through zero.
I cannot see a Type B or A RCD being any more sensitive to this pattern, but both would also work.
I think type A has to have a DC current that crosses zero and a type B just a dc current, including the type A pattern.

Bonding wise the trailer is presumably being used outside so the earth will be a constant potential against different from the supplied earth and so bonding would be pointless.
I would probably earth the trailer instead, with flexible leads being slung about the flex could easily become worn and short to the trailer.

Thanks Richard....and I did mean connection of the earth to the frame rather than bonding. Should know better than to use incorrect terminology lol.
 
I may be bleating up the wrong bush, but am thinking along the lines of distros used in temp supplies for entertainment? each circuit DP protected, everything on RCD. I'm not for one second suggesting that shearing is entertainment! (Though I'm not one to judge!!)
 