TNS system....dual rcd board with 8 circuits...shower 40a... sockets x 2 @ 32a.... lights x 2 @ 6a.... fire alarm @ 16a...security alarm @ 16a.....and a radial circuit for more sockets @ 20a....I was informed by the sunbed people that it has a high starting load of around 9kw so I wanted to cover it by using 10mm t+e a 40a breaker and an isolator in the same room as the sunbed.....cable length from board to isolator is approx. 15 mtrs.
 
Never use a sun bed by the way haha to crash the thread here, I have psoriasis which needs light treatment every year and the nurses who look after the dermatology department also do evening group sessions for people with skin cancer, they told me nearly every person in the group got the disease by using sun beds.
 
TNS system....dual rcd board with 8 circuits...shower 40a... sockets x 2 @ 32a.... lights x 2 @ 6a.... fire alarm @ 16a...security alarm @ 16a.....and a radial circuit for more sockets @ 20a....I was informed by the sunbed people that it has a high starting load of around 9kw so I wanted to cover it by using 10mm t+e a 40a breaker and an isolator in the same room as the sunbed.....cable length from board to isolator is approx. 15 mtrs.


type c 32a
6mm t&e
32a rotary isolator

perfectly fine
 
type c 32a
6mm t&e
32a rotary isolator

perfectly fine
what about the high start up load,could this be the reason for the trip outs

- - - Updated - - -

or will the type c make the difference from using a tybe b because of the breaking capacity
 
what about the high start up load,could this be the reason for the trip outs

- - - Updated - - -

or will the type c make the difference from using a tybe b

type c breaker will handle start up load mate , prob could be the reason
 