50x 100 = 5000watts 21.5amps
1kw fan 4 amps
light .2 of a amp
not even pulling a load a 7.5kw shower would
no power factor adjustment for inductive lighting ?
;-)
50x 100 = 5000watts 21.5amps
1kw fan 4 amps
light .2 of a amp
not even pulling a load a 7.5kw shower would
wasnt having a dig mate , just askingyes I am but not vastly experienced like some of you are.
type c 32aI was told off the sunbed engineer theres a starting load of around 9kw when it fires up
I was told off the sunbed engineer theres a starting load of around 9kw when it fires up
im amazed it works on a 32a mcb without tripping to be honest.
is it a type c mcb ?
TNS system....dual rcd board with 8 circuits...shower 40a... sockets x 2 @ 32a.... lights x 2 @ 6a.... fire alarm @ 16a...security alarm @ 16a.....and a radial circuit for more sockets @ 20a....I was informed by the sunbed people that it has a high starting load of around 9kw so I wanted to cover it by using 10mm t+e a 40a breaker and an isolator in the same room as the sunbed.....cable length from board to isolator is approx. 15 mtrs.
what about the high start up load,could this be the reason for the trip outstype c 32a
6mm t&e
32a rotary isolator
perfectly fine
that's the thing,she said it has tripped a couple of times.
what about the high start up load,could this be the reason for the trip outs
- - - Updated - - -
or will the type c make the difference from using a tybe b