We are considering putting in two glamping pods on our farm.
The main house has a two phase supply (so im told). The house has a annex connected to it and also stables.
The pods will be situated 300 meters from the main consumer unit. Cables would need to be underground.
At the pods we will need to supply lighting and a few sockets for a kettle, toaster 2 ring hob, fridge and hairdryer. (no heating) A klargester sewerage plant will also be present.
We estimate that if everything is running at once we could have a draw of around 4kw.
So my question is simple!!!!!! what size/type SWA would be required. What volt drop would there be etc.
I look forward to anybodies help.
 
We are considering putting in two glamping pods on our farm.
The main house has a two phase supply (so im told). The house has a annex connected to it and also stables.
The pods will be situated 300 meters from the main consumer unit. Cables would need to be underground.
At the pods we will need to supply lighting and a few sockets for a kettle, toaster 2 ring hob, fridge and hairdryer. (no heating) A klargester sewerage plant will also be present.
We estimate that if everything is running at once we could have a draw of around 4kw.
So my question is simple!!!!!! what size/type SWA would be required. What volt drop would there be etc.
I look forward to anybodies help.
You need to get an Electrician to design and provide a quote for the works required, the design will provide all the answers you require, I feel it would be wrong to provide any other advice without a site visit, don't make the mistake of buying cable. the persons you employ will get all the correct cabling and accessories needed, trying to help by buying stuff from an internet enquiry would be a false economy in my book.
 
At 300m and 8kw total load you are looking at a serious wedge of cash on the cable. Id strongly suggest getting a spark in to calculate that, as even one size too big is a LOT more money. Also installing 300m of anything is going to be a massive task, you are going to be talking roughly a tonne of weight.

Have you considered the alternative idea of using camping gas for kettle / hob.12v lighting and fridges and 5v usb sockets supplied from a solar and battery setup? No hairdryer though :)
 
The pods will be situated 300 meters from the main consumer unit. Cables would need to be underground.

We estimate that if everything is running at once we could have a draw of around 4kw.
So my question is simple!!!!!! what size/type SWA would be required. What volt drop would there be etc.
I look forward to anybodies help.

Your question isn't as simple as you think, and one that will be very costly if the answer is wrong, that's a very long cable to have to replace when it turns out to be undersized!

Any answer you get here will only be an estimate and would need the electrician who designs the circuits to confirm the required size. The size of cable will depend on how the circuit(s) are designed, it may be better to install a single circuit, or it may be better to install one for each pod.

At that distance there may be some earthing considerations, again it will be up to the person designing the installation to establish this.

Having said all that, my rough calculations based on my own assessment of the intended load you have described is that something in the region of 95mm conductors may give an acceptable voltage drop for a single circuit to feed both pods.
However I wouldn't install this size cable, I would design this as a parallel feed to reduce costs and reduce the physical size of switchgear required.
 
A 3OOmtr cable run needs to be designed properly, you are looking at a fairly large csa cable

what’s wrong with a couple tents and a gas stove :D
 
Is it worth considering running both phases down a cable to a transformer near the pods.
This would need to be properly designed but volt drop would be roughly half and you could use the right transformer taps to ensure correct voltage at point of use.
 