How far apart are the two glamping pods?
As already covered, you need to be very sure of the total load, and the distances involved, and any plans for the foreseeable future (e.g. any more pods, or any extra facilities like heating), as the installation costs will not be cheap and will cost you a lot more if it is over-specified (or worse and under-specified so has to be replaced).
There are always many way to do something and good engineering is the art of compromise - to meet the goals of safety and functionality at the best price.
With such a cable length you are looking at a lot of metal, and that is expensive, but some of the suggestions still may not be cost-effective in this case. For example, the idea of using 2-core cable from your 480V split supply could save a lot of cable costs, but unless it is well over £1k savings probably won't pay for the transformer. Also transformers have some losses, so trading off the running cost difference may not be so obvious.
You can get aluminium cable but that is rare to see in the UK outside of the electricity supply network and big factories. Aluminium is about 50% higher resistance than copper but much cheaper, so going up a size can still be cheaper in overall cable cost for similar ratings. But it is a pain to work with as usually solid inflexible cores and you need to take special precautions when terminating to avoid galvanic corrosion between aluminium and copper/brass/etc in most equipment. In your case again it looks to be below the point when it would be worth looking at Al cable options (most sparkys would steer clear of that option).
Same for other clever solutions like local power storage to allow a kettle or similar to run at high power for 5-10 minutes with the overall cable load being less for a longer period. While it looks like a neat idea, it probably won't be cost effective and adds a significant reliability question due to the complexity.
So it looks like your best option is going to be just a lot of copper cable. A quick look at the 50mm case would suggest that 2-core cable using the armour for earth is probably just usable with a 40A fuse protecting the feed, but that would very much depend on your supply characteristics. If your supply Ze does not permit that option, it may be most cost-effective to put a time-delay 300mA RCD (or similar) up front to clear cable faults while maintaining selectivity with the galamping circuits on RCBOs, etc., rather than go for 3-core cable to lower R2 as that extra copper core will add something like £4/m to the raw cable cost.